Issue
Have Cyberstations and BCXs and/or 3rd party devices on different subnets
Product Line
Andover Continuum
Environment
- Cyberstations
- BCX 40xx
- 3rd Party MSTP/IP BACnet
Cause
Unable to communicate with B3 devices or get B3 point values.
Resolution
Review LAN configuration. Each separate subnet requires a single BBMD for communication.
See BACnet documentation on line via Cyberstation or "Introducing BACnet" document in Cyberstation.
See Simple BBMD setup.