Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Cannot re-host a Continuum virtual software license

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot re-host a Continuum virtual software license
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • JohnBoehmer
    JohnBoehmer
  • DavidFisher
    DavidFisher
  • JonGreen
    JonGreen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3234 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot re-host a Continuum virtual software license

JohnBoehmer Schneider Alumni (Retired)
‎2019-02-21 09:14 AM

Issue

All efforts to move a Continuum Virtual License from one host machine to another are unsuccessful.

Product Line

Andover Continuum

Environment

Continuum Cyberstation

Cause

  1. The license type is not shown as Re-hostable in the Sentinal Admin Control Center webpage.

    Sentinal Web Page.png

     

  2. The license type is not shown as re-hostable after applying the Re-hosting upgrade activation file received from Andover Upgrade Services.
     
  3. The error Invalid Recipient information, process canceled! is displayed when entering the recipient id file (.id) in the RUS Key Utility. Softkey Invalid recipient error H2H.png

     

  4. The HaspRuntimeForContinuum.exe is the wrong version.

Resolution

  1. Contact Andover Upgrade Services and provide them with a new host information file (.c2v) produced using the RUS Key Utility.
  2. On the host from which the license is to be transferred...
    1. HaspRuntimeforContinuum.exe is the most current version available on Exchange.
    2. Rus Key Utility is the latest version available on Exchange.
    3. Contact Product Support Services for assistance.
  3. On the host the license will be transferred to...
    1. The most current version of HaspRuntimeForContinuum.exe must to be installed prior to using the RUS Key Utility to generate the recipient fingerprint file (.id).
    2. The HaspRuntimeforContinuum must be installed As Administrator.
  4. On the host licensed host…
    1. HaspRuntimeforContinuum.exe is the most current version available on Schneider Electric Exchange.

       

A demonstration of the rehosting process can be viewed here.

Labels (1)
Labels:
  • Andover Continuum
Tags (7)
  • Find more articles tagged with:
  • HASP
  • JohnBoehmer19
  • re-hosting
  • Rehosting
  • RUS
  • Sentinal
  • transfer
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore