Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Cannot bind a SE7000 Series controller to a MPM controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot bind a SE7000 Series controller to a MPM controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Ramaaly
    Ramaaly
  • sesa116873_brid
    sesa116873_brid
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1237 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot bind a SE7000 Series controller to a MPM controller

Picard Product_Support
‎2018-09-06 09:36 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2022-04-05 07:27 AM

Issue

The SE7000 Series controller will not bind to a MPM controller with Building Expert version 2.7. SE7000 controller is not listed in the discovery window when a bind is performed. 

Product Line

EcoStruxure Building Operation, EcoStruxure Building Expert

Environment

  • Building Operation Workstation
  • Building Operation Automation Server
  • SSL SE7000
  • SSL MPM

Cause

It was determined that the SE7000 controller had the old Zigbee module installed. Starting with Building Expert 2.7, the SE7000 Series stats requires the newer Zigbee Pro module in order to connect to the MPM controller.

You can determine if the new module is installed by the part number printed on the Zigbee module. The old Zigbee module has a label with the part number 051-0125R01 printed in it.

Resolution

The older Zigbee module will have to be replaced with the new Zigbee Pro module, and can be field replaced. The newer Zigbee Pro module can be ordered using part number VCM7000V5045P. The actual part number that will appear on the new Zigbee Pro module label is 051-0132R00. 

The module is the smaller PCB board mounted on the left side of the main PCB board. 
1. Remove the SE7000 controller’s cover. 
2. Carefully remove the Zigbee module form the main board.
    * The main PCB board is hinged on the left and is held in place by two tabs on the right 
    * Gently press the tabs to the right to release the main PCB board and swing it open 
    * Gently depress the 2 plastic mounts that hold the Zigbee module to the main PCB board
    * Remove the Zigbee module being careful not to damage the connection pins.
3. Replace with the new Zigbee module (051-0132R00)
4. Replace the cover.
5. Configure the Zigbee network of the SE7000 controller 

You should now be able to discover the SE7000 controller in the MPM.
 

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (2)
  • Find more articles tagged with:
  • 16072
  • RamaAly22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore