Can 2 MSTP Networks be connected to the same Automation Server?
  • Can 2 MSTP Networks be connected to the same Automation Server?
  • Cody_Failinger
    Cody_Failinger
  • PaulFr
    PaulFr
  • CraigEl
    CraigEl
  • SESA116857
    SESA116857
‎2018-09-10 01:13 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:43 PM
How many MSTP networks can you connect to an Automation Server (AS or AS-B)?
  • Version 1.3 and newer
  • MSTP Network on an StruxureWare Building Operation Automation Server (AS or AS-B)
  • BACnet MSTP Devices
Require 2 separate MSTP networks, either to use 2 different Baud rates or to speed up the network and split the devices across the 2 ports.
You can create 2 separate MSTP networks under the BACnet interface of an AS-B or AS (version 1.3 or higher), one on Comm A the other Comm B.
Each can run at different Baud rates if required.
For the number of supported devices please reference, Maximum number using StruxureWare Building Operation (Scalability and Capacity). Please be aware that the listed maximum is for the Automation Server allowing you to distribute between the two comm ports.
Tags (3)
  • 11327
  • b3
  • controllers