CX Ethernet IP Level communications troubleshooting

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • CX Ethernet IP Level communications troubleshooting
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Carl_Slack
    Carl_Slack
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1911 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

CX Ethernet IP Level communications troubleshooting

Picard Product_Support
‎2018-09-11 12:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-09-25 06:46 PM

Issue

CX level controller was once online and now appears as offline

Product Line

Andover Continuum

Environment

  • Continuum
  • Netcontroller
  • CX
  • ACX
  • BCX

Cause

From time to time issues will be reported that controllers are offline at the IP level.

Resolution

Troubleshooting steps to perform:

 

  1. From one of the existing sites Cyberstations perform a ping of the controller. If there are responses, verify that the response is from the controller and not another device. Verification of the response can be done via Wireshark capture if the CX appears to be responding.
  2. If there are responses to the ping, then attempt to open up the web-configuration page for second generation controllers.
  3. Verify the site’s Cyberstation is online itself. (Right-Click/edit the workstation and view the Comm
    Status. It will be either Online or Offline.)
  4. With CyberStation installed on technician’s laptop with the same version as the site version. Plug an Ethernet cable into the same hub the controller is plugged into. Connect to the site database with the local laptop's CyberStation and start Continuum. Check the controller in Continuum Explorer to see if it shows offline to the local laptop's CyberStation. If the controller is online to the local laptop's Cyberstation, then it is clearly a site network issue. At that point we will need to make sure all the IP address info is correct; there is no port blocking, subnet masks, gateways etc… Standard network troubleshooting.
  5. If the controller shows offline to the local laptop's CyberStation, then look at the CPU lights on the
    controller for activity. Watch the link light, CPU, IO bus lights if there is IO modules, etc… If those
    look abnormal and you have a smart phone it will be worthwhile to try and get a video of them to
    send into support for review.
  6. If there is no link light then try disconnecting the Ethernet cable from the NETWORK SWITCH and plug it back in to check if it brings the controller back online.
  7. If that does not bring the controller back online try disconnecting the Ethernet cable from the CONTROLLER and then immediately put it back and check if the controller comes back online.
  8. If all of the above fail then the next step will be to power cycle the controller to try and bring it back online.
  9. If communications cannot be established, contact support and open up a case for additional troubleshooting to determine if the controller needs to be sent to repair.
  10. If communications is restored and further investigation is required, please retrieve the following
    information and open a case with support for review.
    1. Controller error log
    2. Controller offline listview exported to CSV
    3. A Wireshark LAN capture at the controller level with peak traffic occurring
    4. Additional information may be requested including a controller core dump. This is a very
      intensive process. Support will supply the Core Dump Utility if needed.

 

Please click HERE for a copy of these instructions in PDF format.

Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (1)
  • Find more articles tagged with:
  • 12355
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of