Verification of BBMD broadcast table list
Andover Continuum
  • bCX
  • CyberStation
Where is the location of BBMD broadcast table list.
  1. Using a web browser connect to the bCX using the IP address and login.
  2. Select the "BBMD Configuration" option to the left.  (If this in not available then BBMD is not enabled).
  3. The BBMD Configuration page lists the IP address, broadcast mask, and network port for each BBMD that the bCX knows of.
  4. After a successful "Save All To Flash" has been executed from the BBMD Configuration webpage the "Saved" buttons will be checked off.
  5. After a "Teach" has been executed from the BBMD Configuration webpage, the Teach Results webpage will be displayed.
  6. If there is an entry in the BBMD Configuration webpage that has a "rejected" status on the Teach Results webpage, either continue to troubleshoot until the teach is successful or remove that entry from the BBMD Configuration webpage.