Issue
How many BBMDs and Foreign Devices can be registered on a CyberStation and a bCX4040?
Product Line
Andover ContinuumEnvironment
- BACnet
- bCX4040
- CyberStation
- BBMD
- Foreign Device
Cause
Concerned about large BACnet sites and exceeding a limitation on the number of BBMDs and Foreign Devices that can be registered.
Resolution
Maximum number of BBMDs
The maximum number of BBMDs that can be registered on a bCX4040 or on a CyberStation is 32.
Maximum number of Foreign Devices (FDs)
- Continuum v1.93 or earlier
- The maximum number of Foreign Devices (FDs) that can be registered on a bCX4040 or on a CyberStation is 64.
- Continuum v1.94 or later
- The maximum number of Foreign Devices (FDs) that can be registered on a CyberStation is 1024
- The maximum number of Foreign Devices (FDs) that can be registered on a bCX4040 is 64.