BACnet Interface object creation error: Property value out of range

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet Interface object creation error: Property value out of range
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • David_Kendrick
    David_Kendrick
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4523 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet Interface object creation error: Property value out of range

Picard Product_Support
‎2018-09-06 12:05 PM

Last Updated: Admiral David_Kendrick Admiral ‎2022-11-14 03:50 AM

Issue

  • Receive error "Property value out of range" when creating a BACnet interface on the Enterprise Server
     
  • Following problems after upgrading SmartStruxure servers to 1.5:
    • Attaching an Automation Server to or detaching it from an Enterprise Server will fail with “Property value out of range” error.
    • Changes to the ~/System/Interface Manager/BACnet fail to be propagated lead-shadow functions through to the child servers.
    • Automation Server controllers dropping offline following an upgrade to 1.5 (BACnet command priority related  also may see numerous "Changeset Rollback errors")

Product Line

StruxureWare Building Operation 1.1, 1.2, 1.4, 1.5 and above

Environment

  • Enterprise Server (ES) BACnet IP Interface
  • Windows XP, Windows 7 and Windows Server 2008 R2

Cause

Their may be various items that generate this error, checking the Enterprise Server (ES) system log in the Software Administrator may assist in pin pointing the error.  If you see an error that ends with ~/BACnet Interface/IP Network, then this error is generated when their is no valid IP Network. 


For SmartStruxure 1.5 or above or planning to upgrade from 1.4 to 1.5 (and above) 

This issue only occurs if a BACnet interface is used and the site has changed the BACnet "Default Priority Level" from the default value of 16, to 8 or a smaller numeric value in the Automation Server while running in V1.4. The "Property value out of range" message relates to the new Force priority level in 1.5 and the Default priority level in 1.4.1 being mismatched.

Resolution

The ES must be connected to an IP network. To resolve this error follow these steps:

  1. Close all Workstations (if running)
  2. Connect the Enterprise Server to a valid IP network (with a valid IP address).
  3. Stop and Restart the Enterprise Server service through the Software Administrator application.
  4. This should now allow the BACnet Interface to be created successfully

For SmartStruxure 1.5 or above or planning to upgrade from 1.4 to 1.5 (and above)

Please refer to TPA-SBO-14-0005.00

Before upgrading to 1.5 make sure the "Default Priority Level" within the Automation Server is set to 9 or higher. 

If the system has been upgraded with the incorrect values, then:

  1. If the site uses single servers, or the ES/AS communication still operates correctly, then this can be corrected by changing the setting in both the AS and the ES to a value of 9 or higher.
     
  2. If after upgrading a multi server configuration and the AS does not stay online, then a Hotfix can be used fix the problem using the following steps:
    1. Apply the hot fix #1.5.0.4301; available from Product Support Services
    2. Fix the multi-server (by detaching/re-attaching the servers)
    3. Correct the two properties (AS and ES).


WARNING: It is essential for any BACnet system at 1.5 or later that the "Default Priority Level" must have a larger numeric value than the "Force Priority Level, otherwise some BACnet functions may not behave as expected.

Note: This also applies even if the hot fix has been installed.

The effects of not setting the Default above the Force Priority level are:

  1. If Force Priority Level is equal to the Default Priority Level:
    Changing the Value of a BACnet value or a BACnet output object will cause the Value to appear Forced. This applies to the BACnet objects in both SmartStruxure servers and those in 3rd party BACnet devices.
     
  2. If Force Priority Level has a larger numeric value than the Default Priority Level:
    Changing the Value of objects mentioned above will cause the Priority Override icon overlay to be turned on next to the Value property in the WorkStation’s property grid. 
     
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 10960
  • 26027
  • 26190
  • DavidKendrick22
  • defect
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of