Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

BACnet COV subscription system COV Settings

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet COV subscription system COV Settings
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • DavidChild
    DavidChild
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
6547 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet COV subscription system COV Settings

Picard Product_Support
‎2018-09-07 11:20 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:58 PM

Issue

BACnet COV subscription system

Product Line

EcoStruxure Building Operation

Environment

  • BACnet Settings
  • COV subscriptions
  • v1.7 and earlier

Cause

A site will have a problem with the amount of traffic because of misconfigured COV Increments. The problem is that Building Operation, the  ES and AS resubscribes to values every 10 seconds and one by one.
So for example:

hh:mm:ss
00:00:00 Value1
00:00:10 Value2
00:00:20 Value3
00:00:30 Value4
...
05:00:00 Value1800

If you have more than 1800 subscriptions the ES or AS is not able to do all subscriptions in 5 hours.   5 hours is used because Building Operation subscribes to the values with a lifetime of 5 hours.  

Resolution

BACnet COV subscription system is not influenced by the requested transfer rate in the edit bindings system (Subscriptions using BACnet). That is used in the case where the external device does not support COV, and read-property must be used instead.

The design in 1.4 and 1.5 simply did not anticipate such large numbers of COV subscriptions.

Workaround:

  1. 1.Exit Workstation
  2. 2. Stop the Enterprise Server
  3. Edit using notepad the server.properties file located in "C:\Program Files\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\etc\
  4. Find at the bottom:
    # Set GenericConsume communication defaults
  5. Add the two following lines:
    NspServer.BACnetPlugIn.COVSubscriptionLifetime entry = 28800
    NspServer.BACnetPlugIn.COVTimerPeriod entry = 5
  6. Save your changes and close the server.properties file.

This changes the default values from 5 hours to 8 hours and 10 seconds to 5 seconds.

NOTE From version 1.8 the BACnet Interface manager (/Server 1/System/Interface Manager/BACnet) provides access to these settings (COV subscription lifetime (default 8 hours) and Server COV renew rate(default 5 seconds)) The settings will be controlled via the Enterprise Server if connected.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (6)
  • Find more articles tagged with:
  • 1.4.1.2009
  • 14726
  • alm
  • DavidShore20
  • hotfix
  • qc23758
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore