Subscriptions using BACnet
  • Subscriptions using BACnet
  • DavidChild
    DavidChild
  • sesa139513
    sesa139513
‎2018-09-07 08:51 AM
What is the BACnet point data refresh rate and how is the rate changed?
  • Building Operation AS-P and AS-B
Subscriptions are the connection between the value from the BACnet Interface point to the value on the ES or AS.
These subscriptions can be edited using the Binding of the value.
Using 1.4, edit the configuration of the Binding as shown below:
Here, the default 10 seconds interval in the Requested Transfer Rate can be changed. The default is 10 seconds.
This allows changing the default interval of 10 seconds down to a minimum 100 milliseconds a maximum 24 hours:
Using 1.3: Edit the configuration of the Binding as shown below:
Here the default 10 seconds interval in the Requested Transfer Rate can be changed. The default is 10 seconds.