Automation Server CPU usage between 80-100%
  • Automation Server CPU usage between 80-100%
  • sesa139513
    sesa139513
  • RobertAndriolo
    RobertAndriolo
  • Benji
    Benji
  • CraigEl
    CraigEl
  • sesa177673
    sesa177673
‎2018-09-10 07:55 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:15 AM
Automation Server CPU usage goes between 80-100% even with few programs, trends or alarms.
AS Automation Server
Cause 1: BACnet into AS uses a lot of resources
Cause 2: The AS has bindings from a point to a variety of places
Also check out the AS CPU and Memory Loading Quick-Help video on the Exchange.
Example Resolutions in order:
  1. The issue described is Functions as Design in StruxureWare Building Operation. The AS results with high CPU percentage with just one point from BACnet interface loaded; however, it had no effect on AS performance.
  2. Check the propagation of values. An example would be a Space Temperature which is required by the field bus, the BACnet interface, LON interface, etc. Make sure to properly disseminate this value so to avoid overloading the CPU.
  • 7469