Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Archiving and SQL database size keeps growing

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Archiving and SQL database size keeps growing
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • RobertAndriolo
    RobertAndriolo
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2383 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Archiving and SQL database size keeps growing

Picard Product_Support
‎2018-09-11 05:13 AM

Issue

Archiving and database size with FIFO not working

Product Line

TAC INET

Environment

I/NET site

Cause

dbo.Events keeps growing and presumably is not in FIFO mode (First In First Out)

Resolution

Note: Autogrowth is not used with TAC I/NET Seven or TAC Andover Continuum
The size of the InetDB can be set through Microsoft SQL Server Management Tool:  

  1. By selecting the InetDB database properties you can set the Autogrowth setting via the Files page.  Under the Autogrowth column select the browse button as shown:

     
  2. The Change Autogrowth setting by either disabling the Autogrowth check box or you can set Autogrowth to a Maximum File Size as shown:
     
     
  3. The Autogrowth value now shows this setting is restricted to setting define in step 2.

 

Disabling Autogrowth allows the events to be removed from the table when the total size of the SQL database reaches the limitation set in the properties of the db.

The table dbo.Events has all the current events and it should be the biggest. The dbo.currenteventdetail table keeps up with the current max events and the current minimum events. Lets say it is around a million (1,000,000) events and so the first event in this table would be 01 and the last would be the 1000000. If items are removed from the other table, the dbo.Events, then this other table, the dbo.currenteventdetails is off. This means we run the risk of losing those events that are not correctly numbered.

Manually removing items from one table can have an impact on other tables and how this data is kept and archived.

About archiving and shrinking the db, this is a function of SQL. SQL goes into a FIFO mode, which means First In, First Out. This keeps the db from getting to large. The archived records are designated as archived in the db and even though they are still (secretly) in the db, they will be out as soon as the db is over the capacity amount and the amount designated in the db.currenteventdetail table is the guide for what is current.

The thing that keeps the db from getting to large is the archive is setup correctly and old data is archived. It is still available via Reports, but considered not technically in the db. That is what shrinks the db and keeps it from getting over size. 

 

Note: Autogrowth is not used with TAC I/NET Seven or TAC Andover Continuum

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (1)
  • Find more articles tagged with:
  • 13600
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore