Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

All inputs on a Continuum Infinet controller read 999.99 when viewing the electrical value

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • All inputs on a Continuum Infinet controller read 999.99 when viewing the electrical value
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • ScottLeedberg
    ScottLeedberg
  • sesa119747
    sesa119747
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3331 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

All inputs on a Continuum Infinet controller read 999.99 when viewing the electrical value

Picard Product_Support
‎2018-09-06 02:46 PM

Last Updated: Admiral David_Kendrick Admiral ‎2023-05-02 07:15 AM

Issue

All inputs on an Continuum Infinet controller read 999.99 when viewing the electrical value "elecvalue"

Product Line

Andover Continuum

Environment

Infinet Controller

Cause

This indicates that the internal voltage reference is "out of range".

Resolution

  1. Verify that inputs coming from external transducers are not exceeding the voltage input range, either 5 or 10 volts depending on model, if so use a voltage divider on the input. 
  2. Verify that any input wiring is not run in the same conduit as high voltage cable, or is properly shielded and grounded.  If there is voltage getting coupled into the input wiring, separate the input wiring from the interference, or shield the cables.  If the interference is being caused by the end device such as an auxiliary contact from a high voltage device, a cap between .01 and 1 microfarads across the input terminal to earth ground may alleviate the problem.
  3. Remove field I/O wiring from the controller and recheck operation.  If the problem goes away determine which I/O wire is the culprit and correct it.
  4. Power down the Infinet controller and restart while connected to network.  This will eliminate this unit having a duplicate ID on the network and it will also run the power up diagnostics. 
  5. Verify proper grounding at the Infinet controller on the AC power terminals, poor grounding can cause erratic operation and communication problems.  The easiest method to verify ground is to connect a digital voltmeter between the earth ground terminal on the powerstrip of the controller and the shield of the Infinet.  This method will only work if you have connected your shields all through the network back to the Infilink and CX controller.
  6. Lastly, a board or controller replacement may be necessary
Labels (1)
Labels:
  • Andover Continuum
Tags (7)
  • Find more articles tagged with:
  • 3101
  • 999
  • capacitor
  • controller
  • DavidKendrick23
  • infinet
  • shielding
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore