Issue
All inputs on an i2920 controller read 999.9 volts even when all input connections are removed. The controller error log shows error number 0x00002809.
Product Line
Andover Continuum
Environment
- i2920
Cause
The 0x00002809 error is logged by the Analog to Digital conversion process when the V Zero is greater than the V Reference. This would indicate a controller calibration failure or a controller hardware failure.
Resolution
The controller should be returned for repair.