All controller inputs read 999.9 volts and controller error log shows error number 0x00002809
  • All controller inputs read 999.9 volts and controller error log shows error number 0x00002809
  • AdamSteele
    AdamSteele
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 12:14 PM
All inputs on an i2920 controller read 999.9 volts even when all input connections are removed. The controller error log shows error number 0x00002809.
Andover Continuum
  • i2920
The 0x00002809 error is logged by the Analog to Digital conversion process when the V Zero is greater than the V Reference.  This would indicate a controller calibration failure or a controller hardware failure.
The controller should be returned for repair.