Alarms stay in the alarm view, they cannot be acknowledged, and do not clear
  • Alarms stay in the alarm view, they cannot be acknowledged, and do not clear
  • Jonas_Brissman
    Jonas_Brissman
  • PeterEdvik
    PeterEdvik
  • Benji
    Benji
  • sesa125819
    sesa125819
‎2018-09-10 03:56 AM
Last Updated: Janeway PeterEdvik Janeway ‎2021-09-29 05:08 AM
Changing the name of a folder under which there is an active alarm, causes an incorrect "Source" path in the alarm message
Building Operation Workstation version 1.8 or earlier
If a folder name is changed it will be correctly updated, but if an active alarm is located  in its sub-folders , then the alarm source path will not be updated.
Initial alarm before the folder name is changed, notice the source ...... FF IV/Trendloggar ......
The alarm after the folder name has been changed FF IV TEST, the / between FF IV TEST and Trendloggar is missing.
If the alarm has not been acknowledged, and clears a second entry for the alarm is displayed in the alarm view.
This is fixed in SBO/EBO 1.9 and later versions.
For versions 1.8 or earlier:
Before updating a EcoStuxure Building Operation(EBO) folder name, check to see if there are any active alarms with a source path that use this folder. If there are, try to clear these alarms.
If a EBO folder name has been changed and there are alarms in the alarm view which cannot be cleared, then use the "Recheck" command to clear them.