Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Alarms are being logged but are not being delivered to all Cyberstations

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Alarms are being logged but are not being delivered to all Cyberstations
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • BillNeville
    BillNeville
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1836 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Alarms are being logged but are not being delivered to all Cyberstations

Picard Product_Support
‎2018-09-06 02:52 PM

Issue

Alarms are being logged but are not being delivered to all Cyberstations

Environment

CyberStation, MSMQ

Cause

MSMQ issues

Resolution

When enhanced alarm delivery is selected and Cyberstations are taken offline, they will not receive alarms until Cyberstation is restarted. Occasionally you can get into a state where even though Cyberstation has been restarted you no longer receive alarms and there are a lot of messages building up in the MSMQ queues.

Event Notifications
Eliminate Cyberstations that no longer exist or are often offline and are setup as recipients on event notifications. These Cyberstations should be removed as recipients to avoid alarm messages from building up in the MSMQ queues.

Three Reasons MSMQ does not deliver messages and some analysis tools
According to MS there are several reasons why MSMQ messages do not get sent/received and in order of precedence are Connectivity, Security and Resource depletion

  1. Connectivity
    1. In Control Panel>Administrative Tools>Computer Management>Services & Applications>Message Queuing>Private Messaging>accalarmchannel, columns can be added to the queue messages line by right clicking, select View, add/remove columns Add Recipient queue and Response queue
      This gives you visibility into what workstations are receiving messages
    2. Ping - The amount of time that a ping test takes to respond can indicate a problem, as can the fact that such a test succeeds only intermittently. (The latter would indicate such issues as name resolution failing and the computer falling back to doing broadcasts for name resolution or network saturation). ping machinename -t this will run until stopped by pressing Ctrl-C, some baselines on each of the machines to the other machines would be good. Once a machine starts building up messages in queues, perform this ping command again to see if there's a difference.
    3. Ethereal (now Wireshark)
      Use Ethereal on one of the machines that is building up messages in a queue, it would be helpful to get an ethereal capture to look at the MSMQ traffic.
  2. Security
    • A Firewall can affect MSMQ delivery. Some firewalls allow configuration down to which specific machines are allowed for the MSMQ service. Here's a Microsoft link to what ports need to be opened for MSMQ in addition to what we require for Continuum. http://support.microsoft.com/kb/183293
  3. Resources
    1. MSMQ has a size limitation for the total amount of space used by queuing messages. If this total size has reached 1.4 Gig then more than likely the storage capacity of MSMQ has been exceeded and the MSMQ service may not start and therefore not deliver messages.
      Determine if the MSMQ capacity has been exceeded
      On each of the WS that should receive messages, go to My Computer c:\windows or c:\WINNT\system32\msmq\storage, right click on the storage folder and go to properties, note the Size.
      1. Perfmon- is a utility that can be run to take a look at resources on a machine and the MSMQ Service attribute Total Message can be added.
      2. Go to Start> Settings> Administrative Tools> Double click on Performance
      3. Keep the defaults that are listed, there should be 3 items listed for memory, Physical Disk and Processor
      4. Click on the "+" button to add a counter
      5. In the performance object drop down, select MSMQ service and under Select counters, select "Total messages in all queues"
      6. Click Add, then Click Close
      7. Right click on Total Messaging and select properties, select a color and width that will stand out, click Ok
      8. Keep an eye on the resources that are being used and adjust the machine or add resources accordingly.
    2. Logging - if it is determined that you need to log some of this info, there are some additional instructions from Microsoft on doing that at http://support.microsoft.com/kb/150934
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2869
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore