Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Adding a Xenta Server to a Vista System for I/NET to Vista Integration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Adding a Xenta Server to a Vista System for I/NET to Vista Integration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Derrick_Ratliff
    Derrick_Ratliff
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1178 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Adding a Xenta Server to a Vista System for I/NET to Vista Integration

Picard Product_Support
‎2018-09-10 12:52 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 06:07 PM

Issue

Adding a Xenta Server to a Vista System for I/NET to Vista Integration

Product Line

TAC INET, TAC Vista

Environment

  • I/NET
  • Vista
  • Xenta 527
  • I2V

Cause

For systems with both I/NET security and Vista HVAC, this allows for a single point to monitor alarms.

Resolution

At least one of the routers on the I/NET system must be a Xenta 527 Web Server.

  1. Start Vista Server
  2. Open Vista Workstation
  3. Right click on the Vista Server object and select New>Device>Xenta 527
  4. Name the Device
  5. Right Click on the Xenta Server Object and select Edit. XBuilder will open 

If your 527 already has an XBuilder Project File  

  1. Select Project>Get From Target
  2. Enter the IP address of the 527 and the root password
  3. Select Get the Full Project
  4. Click on the I/NET object and verify settings have imported  

If your 527 does not already have an XBuilder Project File

  1. Click on the TAC_Xenta_527 root object in the Network Pane
  2. Add the TCP/IP and SMTP settings as required
  3. Click on the I/NET object
  4. Add the I/NET link information and reference hosts
  5. Right click on the I/NET object and select Insert TAC I/NET Network
  6. Click Add Files
  7. Add all save files for that link
  8. Click Ok
  9. Select Vista Database>Save  

You will need to repeat this process for all I/NET links to have full I/NET integration into Vista.

See Additional settings necessary to receive Vista Alarms from an I/NET point to configure Alarms.

Labels (2)
Labels:
  • TAC INET
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5496
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore