Adding a TAC Xenta device to an existing TAC Xenta group

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Adding a TAC Xenta device to an existing TAC Xenta group
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1918 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Adding a TAC Xenta device to an existing TAC Xenta group

Picard Product_Support
‎2018-09-06 03:16 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:10 AM

Issue

If I add a TAC Xenta device to an existing TAC Xenta group, do I have to update other Xenta devices as well?

Product Line

TAC Vista

Environment

  • Xenta programmable controller (e.g. 401, 301, 281)
  • Xenta groups
  • TAC Vista system plugin

Cause

Each programmable Xenta device needs to know the name of all the other Xenta groups, as well as all the Xenta device names in its own group.

Each time a new group member is added, all Xenta devices in that group need to be downloaded. If a new Xenta group is added, all Xenta devices in all groups need to be downloaded.  

This provides new network description files to the controllers so they can communicate properly.

Resolution

All Xenta devices in that group must be updated. LonMaker or NL220 and your Vista databases need to be updated as well.

TAG bindings will also need to be added to the new TAC Xenta device if an LNS database is being used. The TAC Vista System plugin has the feature under the LNS Network menu. "Create Group Bindings"

If this is a large site this will take some time and cause offline devices during this process.

In this case, these bindings can be added manually to the new controller. This will prevent all the other devices having there TAG bindings deleted and the new TAG bindings created.

The following articles show the process for manually adding TAG bindings.

  • Manually adding a Xenta Device with Group bindings in NL220
  • Manually Adding Xenta device with Group bindings in Lonmaker
Labels (1)
Labels:
  • TAC Vista
Tags (4)
  • Find more articles tagged with:
  • 1522
  • MikaelKrantz19
  • PeterEdvik20
  • PeterLarsen20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore