Manually Adding a Xenta Device with Group Bindings in NL220
  • Manually Adding a Xenta Device with Group Bindings in NL220
  • Jonas_Brissman
    Jonas_Brissman
  • PeterLarsen
    PeterLarsen
‎2018-09-06 03:57 PM
Last Updated: Administrator CraigEl Administrator ‎2025-10-27 07:59 PM
When managing a large site, adding a new Xenta controller can be time-consuming if using the System Plug-in to create group bindings. This process often requires taking controllers offline. This article outlines a manual method to add group bindings efficiently without downtime.
TAC Vista
  • TAC Vista Server
  • NL2220
The manual method is effective and reliable if the steps are followed correctly. It allows integration of a new Xenta controller into existing TAG 0 and TAG 1 bindings.
Follow these steps to manually bind a new Xenta controller in NL220:
Step 1: Enable Message Tags Connections Tree
  • Open NL220 and go to Project Settings.
  • Under the Trees tab, enable Message Tags Connections Tree.
  • This will add a new tree view labeled Message Connections.
Step 2: Add to TAG 0 Binding
  • In the Message Connections tree, locate the TAG 0 connection (covers all Xenta controllers).
  • Right-click TAG 0 and select Edit.
  • In the Connection Window, switch to Subsystem View.
  • Drag the TAG 0 from the new Xenta controller into the window.
  • Click Update to apply changes to the database.
Step 3: Add to TAG 1 Binding
  • Locate the appropriate TAG 1 Xenta group for the new controller.
  • Identify the correct TAG 1 connection by the controller name.
  • Right-click the TAG 1 connection and select Edit.
  • Drag the TAG 1 from the new Xenta controller into the window.
Tags (2)