Access Expert BACnet object integration with Continuum and EBO
  • Access Expert BACnet object integration with Continuum and EBO
  • Alan_Wood
    Alan_Wood
  • CraigEl
    CraigEl
Admiral Alan_Wood Admiral
‎2022-10-24 05:31 PM
on ‎2022-10-24 05:31 PM
Information needed for Integrating Access Expert BACnet objects into Continuum and EBO
EcoStruxure Access Expert
Access Expert V3 Hosted
Andover Continuum
BACNet
BACnet objects from Access Expert may show in Andover Continuum, but will not function. An integration using EcoStruxure Building Operation is needed.
  1. BACnet objects from Access Expert may show in Continuum when a BACnet discovery is done, but they will not function.
  2. An integration using EBO with a SmartConnector is required to use Access Expert BACnet objects. Further details on the EcoStruxure Access Expert Smartconnector are available from the Exchange Marketplace.