Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

AS supports network authentication via Radius Server (IEEE 802.1X)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • AS supports network authentication via Radius Server (IEEE 802.1X)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3015 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

AS supports network authentication via Radius Server (IEEE 802.1X)

Picard Product_Support
‎2018-09-06 10:26 AM

Last Updated: Administrator CraigEl Administrator ‎2023-06-07 07:29 PM

Issue

Does the Automation Server support network authentication via Radius Server (IEEE 802.1X)?

Product Line

EcoStruxure Building Operation

Environment

Building Operation Automation Server

Cause

AS supports network authentication via Radius Server (IEEE 802.1X)?

Resolution

RADIUS and IEEE 802.1X are not the same thing, although they can be used together.


Remote Authentication Dial In User Service (RADIUS) is a networking protocol that provides centralized Authentication, Authorization, and Accounting (AAA) management for computers to connect and use a network service. RADIUS is a client/server protocol that runs in the application layer, using UDP as transport.

 

The RADIUS server is usually a background process running on a UNIX or Microsoft Windows server.

RADIUS serves three functions:

  • to authenticate users or devices before granting them access to a network,
  • to authorize those users or devices for certain network services and
  • to account for usage of those services. 

IEEE 802.1X is an IEEE Standard for port-based Network Access Control (PNAC). It is part of the IEEE 802.1 group of networking protocols. It provides an authentication mechanism to devices wishing to attach to a LAN or WLAN. It is a mechanism used in (mostly) switches and wireless access-points to allow or block devices to access the network (or granularly allow access to parts of it).

 

For example, if you have a network port in a meeting room, you can enable 802.1x on the switch port and configure it in such a way that when an employee connects they have access to the entire network, but if a guest connects (with a temporary password) they can only reach the Internet and if a passer-by is tempted to try his luck, they cannot access anything at all.


Does IEEE 802.1X also use RADIUS as it's underlying authentication mechanism?

Yes and no. IEEE 802.1x uses Extensible Authentication Protocol (EAP), the drawing below shows that for wired 802.1x:

  • EAP over LAN (EAPoL) is used between the Supplicant (software on a computer) and the Authenticator (switch).
  • EAP is then usually tunneled over Radius between the Authenticator and the Authentication Server, but it can also be done over Diameter (the successor to Radius).

For wireless, it is similar in the sense that there is also no Radius between the supplicant and the authenticator, only between the authenticator and the Authentication Server (to tunnel the EAP).

802.1X_wired_protocols.png


From EBO 2022 the AS-P and AS-B can be configured as supplicants on a network protected by IEEE 802.1X security. See the IEEE 802.1X Security Webhelp topic for further details.

 

Note: MPx/RPx do not support 802.1x network authentication, see the SpaceLogic controllers MPx/RPx do not support 802.1x network authentication Knowledge Base article  for further details.

 

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 13166
  • CraigEllis22
  • CraigEllis23
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore