ARCNET Controller Ping Returns 'Destination Host Unreachable' Error
  • ARCNET Controller Ping Returns 'Destination Host Unreachable' Error
  • CraigEl
    CraigEl
‎2018-09-09 09:36 PM
Last Updated: Administrator CraigEl Administrator ‎2025-11-04 08:55 PM
When attempting to ping an ARCNET controller from a server using the DOS ping command, the operation fails with the error:
"Destination host unreachable"
Satchwell BAS & Sigma
Satchwell Sigma
This issue typically occurs due to incorrect or missing routing configurations. Specifically:
  • The route to the ARCNET sub-net is not defined.
  • Sigma DNN broadcasts RIP v1 messages for the Sigma server to interpret.
  • By default, RIP Listener is disabled on Windows XP and later systems, preventing dynamic route updates.
To resolve this issue, follow one or both of the steps below:
  1. Enable RIP Listener on the Server
    • This allows the Sigma server to receive and process RIP v1 messages from the DNN.
    • Refer to: Sigma server communication to ARCNET/Ethernet sub-nets via a DNN failing
  2. Add Persistent Routes to the Sigma Server
    • Manually define static routes to ensure reliable communication with ARCNET controllers.
    • Refer to: Persistent routing on the Sigma server
  • Satchwell BAS & Sigma
Tags (2)
  • 5233
  • CraigEllis25