Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

AMT messages: Ind. D/L failed & DCU Queue ovflw

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • AMT messages: Ind. D/L failed & DCU Queue ovflw
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1415 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

AMT messages: Ind. D/L failed & DCU Queue ovflw

Picard Product_Support
‎2018-09-10 06:34 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:52 PM

Issue

AMT messages: Ind. D/L failed & DCU Queue ovflw

Product Line

TAC INET

Environment

  • I/NET Site
  • Download failed
  • Queue Overflow

Cause

Failure to communicate in C-LAN and SubLan

Resolution

For the Ind. D/L failed message in AMT, as well as SCU Lost, is from the Host Workstation. It is telling us that there was an error in downloading individual's information to the SCU.

Explain and define I/NET Ethernet, C-LAN, and Sub-LAN communication has a drawing of a simple INET network, and how it is connected with labels for the names to help with understanding and terminology. Please note the resistors mentioned and make sure your site has these.

Firmware: Check to make sure the same Firmware revision for the INET version you are running is in all the controllers. The DCU7798C is experiencing communication failure. Take a moment to check this as well as from 7798C to the SCU, check the resistors which are shown in the drawing, check the wiring, firmware, etc. That will resolve this failure. If you look closely at the screen shot, it even shows this is a door controller with exceptionally poor communication to the 7798C. It shows the door points. This shows you where to start with the troubleshooting.

Distance: What is the distance between the controllers? I recommend the resistors on long runs or if you have a lot of controllers. If you have more than these two or they are a long way apart, then resistors, yes. If they are 2 meters from each other and it is just these two, then not that critical. The issue appears to be with the CLAN. The pulling down the communication is producing these errors. Check to make sure the wires are protected in conduits and not running along side power or Power-Over-Ethernet, or ballasts. These items can cause interference, which can cause this failure.

Earth Ground: Is the issue on one or between two 7798Cs that are wired the same way? The second 7798C is probably giving the problems. The issue is no earth ground wire on the three terminal power plug. This is the ground that is used on the CLAN comm circuit. There will be LAN Reconfiguration from ALM, the second 7798C is failing on the CLAN communications.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 6867
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of