Issue
Replaced an AC1Plus with an AC1 and the reader pattern is incorrect
Product Line
Andover Continuum
Environment
- Continuum
- AC1
- AC1A
Cause
The AC1/AC1A module only has 1 LED pattern which is Alternate LED pattern, there is no way to alter this.
See Description of LED patterns on access readers, and how to change them for description of LED patterns.
Resolution
If a different LED pattern is required by the site then use an AC1 plus or an ACX57xx which gives the ability to use an alternate LED pattern. See Description of LED patterns on access readers, and how to change them for configuration.