Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

A method to remove access from a large number of Personnel by changing the Expiration Date using a Template.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • A method to remove access from a large number of Personnel by changing the Expiration Date using a Template.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2141 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

A method to remove access from a large number of Personnel by changing the Expiration Date using a Template.

Picard Product_Support
‎2018-09-11 06:00 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:57 AM

Issue

A method to remove access from a large number of Personnel by changing the Expiration Date using a Template.

Product Line

Andover Continuum

Environment

Continuum Access Control

Cause

Need to know how to disable large numbers of Personnel at one time using the Personnel Expiration Date.

Resolution

The Personnel Expiration Date is distributed down to the Controllers and used to allow or deny access at the Door. If a future date is set then the Personnel has normal access, if a past date has been set then they do not have access and a "Person Expiration Date Passed" error will be displayed when they are refused access. See the steps below on how to use a template to mass set this Expiration Date field for a large number of Personnel at the same time.

 

1. Create a Personnel Template in the Personnel Templates Folder. Notice that the Expiration Date defaults to a future date of "12/31/2099 11:59:59 AM".

2. Go to the Attribute Data Source tab and set the ExpirationDate attribute to InheritFromTemplate.

2. PTemplate - ExpirationDate (InheritFromTemplate).jpg

3. Use this Template to create your Personnel objects.

4. Notice that Personnel created from this template should show the Expiration Date in Blue which is also un-editable in the Details tab.

5. Edit the Template and change the Expiration Date to a date that has already past. After saving the Template the changes will be made to all attached Personnel and those Personnel distributed to all online controllers. Viewing the Distribution Properties, you should see an entry for each object refreshed by the Template.

6. Looking at the Access Distribution View you should see that the Personnel have been redistributed down to the controllers successfully.

7. Test your Personnel at the Door and they should no longer have access. Looking in an active Event View you can see that the Personnel are not being granted access with the Message "Person Expiration Date Passed". When setting the ExpirationDate back to a future time they will now have normal access.

Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (1)
  • Find more articles tagged with:
  • 14332
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore