A curve block will not work as expected in a Menta application
  • A curve block will not work as expected in a Menta application
  • Jonas_Brissman
    Jonas_Brissman
  • PeterLarsen
    PeterLarsen
‎2018-09-07 02:29 PM
Last Updated: Spock PeterLarsen Spock ‎2025-05-05 05:45 PM
Even though the curve block is set to range between 0-100, the block just stays at a fixed output somewhere in the curve output range.
TAC Vista
Vista Workstation
The curve requires the first entry of the X value to be the lowest value, and then the subsequent values to be larger than the previous X entry.
Adjust the order of the XY entries on the curve block so the first entry in the X will be the lowest value.
Example of Incorrect Curve
Here is an example of a Curve that will not work. Note the first X entry is -2 and the last X entry is -6.
Example of Correct Curve
To correct this curve, -6 is the lower number, so this should be the first X entry. Here is an example of the curve that has the correct X entry order.
Labels (2)
Tags (2)
  • 15308
  • JonasBrissman25