Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

1.8k Thermistor Compatibility with Xenta Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • 1.8k Thermistor Compatibility with Xenta Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MikaelKrantz
    MikaelKrantz
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6401 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

1.8k Thermistor Compatibility with Xenta Controllers

Picard Product_Support
‎2018-09-06 02:18 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-28 05:14 PM

Issue

Certain Xenta controllers and I/O modules are compatible with 1.8k thermistor temperature inputs. Users often seek clarification on which models support this and the specific temperature vs. resistance characteristics.

Product Line

TAC Vista

Environment

  • Xenta 122-FC
  • Xenta 122-HP
  • Xenta 121-FC
  • Xenta 121-HP
  • Xenta 200
  • Xenta 300
  • Xenta 420A
  • Xenta 450A

Cause

Users need to understand the temperature vs. resistance curve for the 1.8k thermistors used in Xenta controllers, especially for the Xenta 300 series.

Resolution

All Xenta controllers and I/O modules except the Xenta 102-AX use the same 1.8k thermistor type: 1.8KA1.

Below is a summarized Temperature vs. Resistance table for the 1.8KA1 thermistor:

Temp (°C) Minimum kΩ Nominal kΩ Maximum kΩ
-50.0   60.87  63.88  67.03 
-45.0   45.41  47.5   49.68 
-40.0   34.23  35.68  37.2  
-35.0   26.04  27.07  28.13 
-30.0   19.99  20.72  21.47 
-25.0   15.48  16.0   16.54 
-20.0   12.09  12.46  12.84 
-15.0   9.512 9.779 10.05 
-10.0   7.541 7.733 7.929
-5.0   6.021 6.16  6.301
0.0   4.84  4.94  5.042
5.0   3.916 3.988 4.061
10.0   3.189 3.24  3.293
15.0   2.612 2.649 2.686
20.0   2.151 2.177 2.209
25.0   1.782 1.8   1.818
30.0   1.478 1.496 1.514
35.0   1.233 1.25  1.267
40.0   1.033 1.049 1.065
45.0   0.8698 0.8848 0.9001
50.0   0.7357 0.7497 0.7639
55.0   0.6251 0.638 0.6511
60.0   0.5334 0.5453 0.5573
65.0   0.457 0.4679 0.479
70.0   0.3931 0.4031 0.4132
75.0   0.3395 0.3485 0.3578
80.0   0.2942 0.3025 0.311
85.0   0.2559 0.2634 0.2712
90.0   0.2233 0.2302 0.2373
95.0   0.1956 0.2019 0.2083
100.0   0.1718 0.1775 0.1835
105.0   0.1514 0.1566 0.1621
110.0   0.1338 0.1386 0.1436
115.0   0.1186 0.123 0.1276
120.0   0.1054 0.1095 0.1136
125.0   0.094 0.0977 0.1015
130.0   0.084 0.0874 0.0909
135.0   0.0753 0.0784 0.0816
140.0   0.0676 0.0705 0.0735
145.0   0.0609 0.0635 0.0663
150.0   0.0549 0.0574 0.0599
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4279
  • MikaelKrantz25
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore