"Time Constant" and "Backup" for Analog input in Menta

Ask the Community

Ask questions, get advice from experts and peers on Digital Automation & Energy Management.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Support
  • Ask the Community
  • "Time Constant" and "Backup" for Analog input in Menta
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
35
chris_clerc
Administrator chris_clerc Administrator
8
MikaelKrantz
Guinan MikaelKrantz Guinan
7
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Ask the Community
Start a Topic
Solved
Makarand988
Crewman Makarand988
Crewman

Posted: ‎2022-11-25 05:04 AM

0 Likes
3
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-25 05:04 AM

"Time Constant" and "Backup" for Analog input in Menta

Hi

I am using schneider SHD100 -T Temperature + RH sensor 

I am curious to know about the "Time Constant"  and "Backup" in Analog Input.

Information is there in Menta Web help but I didnt understand.

If I keep it too high for example 100 sec, so what will happen ?

What value should I consider as rule of thumb for "Time Constant" ?

Does it affect the accuracy of the sensor ?

What does mean by "Backup" check box while creating analog input in Menta.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MikaelKrantz
Guinan MikaelKrantz Guinan
Guinan

Posted: ‎2022-11-27 10:05 PM

0 Likes
2
1621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-27 10:05 PM

First the Backup.

 

This is to be able to store the value over a power failure.

However, if you use it for reading a sensor, it will read the actual value of the sensor, so no use in this scenario. 

If the AI block is set as Constant value, then you may select the Backup flag.

 

Time Constant

 

This is a first order filter to make it possible to slow down rapid changes. 

Should use like 5 or 10 seconds, depending on what type of signal you are reading, others may use other values.

Could be used like noise reduction...

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
MikaelKrantz
Guinan MikaelKrantz Guinan
Guinan

Posted: ‎2022-11-27 10:05 PM

0 Likes
2
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-27 10:05 PM

First the Backup.

 

This is to be able to store the value over a power failure.

However, if you use it for reading a sensor, it will read the actual value of the sensor, so no use in this scenario. 

If the AI block is set as Constant value, then you may select the Backup flag.

 

Time Constant

 

This is a first order filter to make it possible to slow down rapid changes. 

Should use like 5 or 10 seconds, depending on what type of signal you are reading, others may use other values.

Could be used like noise reduction...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Makarand988
Crewman Makarand988
Crewman

Posted: ‎2022-12-05 06:57 AM

In response to MikaelKrantz
0 Likes
1
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-05 06:57 AM

Hi

 

 

 

Please refer below snap from the data sheet of SHD100-T. Does it indicate that should I use Time Constant = 15 Sec

 

 

 

 

Screenshot_20221205_202532.jpg

 

 

 

 

 

 

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

MikaelKrantz
Guinan MikaelKrantz Guinan
Guinan

Posted: ‎2022-12-05 07:21 AM

In response to Makarand988
0 Likes
0
1579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-05 07:21 AM

Well, you can use 15 seconds as well.

 

However that value is for the sensor, how long time it takes for a change of temp to affect the value...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore