What is the cause of getting a negative reading for the active power (W) in powerlogic PM21000, and how i can to change the mode from export to import
Metering & Power Quality
  • EcoStruxure Power & Grid
  • What is the cause of getting a negative reading for the active power (W) in powerlogic PM21000, and how i can to change the m...
Charles_Murison
Picard Charles_Murison Picard
526
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
bada
bada
Cadet
Posted: ‎2023-05-15 01:28 PM
1
974
Charles_Murison
Posted: ‎2025-03-27 08:39 AM
Hello @bada ,
There could be many reasons why you are seeing negative power. The most common reason is CTs are installed backwards, the next most common reason is the CTs and voltage connections are not on the same phase. Example: A phase voltage however B phase CT.
Suggest looking at the phase angles between voltage and current to determine if you have a wiring issue.
Charles
Charles_Murison
Hello @bada ,
Charles