SLPSLXX needs a modbus line terminator?
Metering & Power Quality
  • EcoStruxure Power & Grid
  • SLPSLXX needs a modbus line terminator?
Charles_Murison
Picard Charles_Murison Picard
522
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
136
Ramasamy_N
Captain Ramasamy_N Captain
115
Posted: ‎2022-07-18 04:46 AM
1080
I´m working in a project for BMS, where many SLPSLXX are used. Those sensor are coneccted in a modbus net to the RP-C, via sensor bus port. I know that all the modbus lines needs at both ends a 120 ohm resistor, but I didn´t find any document about how to do it on this system.
I would be grateful if someone could confirm if I need the bus end resistor or not.
PiotrJakubczyk
Sisko PiotrJakubczyk Sisko
Sisko
Posted: ‎2022-08-03 02:22 AM . Last Modified: ‎2022-10-19 12:43 AM
Here is explanation
https://e2e.ti.com/blogs_/b/analogwire/posts/rs-485-basics-when-termination-is-necessary-and-how-to-...
But i Think from your point of view it is more important to know this:
The RP-C Modbus network supports up to 10 connected Modbus devices with the following restrictions:
  • Maximum of one KNX Modbus gateway (RP-C-EXT-KNX)
  • Maximum of 250 Modbus registers
NOTE:
The RP-C Modbus network does not support 64-bit Modbus registers.
https://community.se.com/t5/Building-Automation-Knowledge/What-is-the-BACnet-MSTP-unit-load-of-the-S...
Also
Ensure that the total length of the room bus does not exceed 72 m
Ensure that the total length of the sensor bus does not exceed 61 m
Also more proper forum is "
  • EcoStruxure Building Operation Forum