Posted: 2022-07-18 04:46 AM
Link copied. Please paste this link to share this article on your social media post.
I´m working in a project for BMS, where many SLPSLXX are used. Those sensor are coneccted in a modbus net to the RP-C, via sensor bus port. I know that all the modbus lines needs at both ends a 120 ohm resistor, but I didn´t find any document about how to do it on this system.
I would be grateful if someone could confirm if I need the bus end resistor or not.
Link copied. Please paste this link to share this article on your social media post.
Here is explanation
But i Think from your point of view it is more important to know this:
The RP-C Modbus network supports up to 10 connected Modbus devices with the following restrictions:
Maximum of one KNX Modbus gateway (RP-C-EXT-KNX)
Maximum of 250 Modbus registers
The RP-C Modbus network does not support 64-bit Modbus registers.
Also
Ensure that the total length of the room bus does not exceed 72 m
Ensure that the total length of the sensor bus does not exceed 61 m
Also more proper forum is "