Pulse on time - Power Meter PM5300
Metering & Power Quality
  • EcoStruxure Power & Grid
  • Pulse on time - Power Meter PM5300
Charles_Murison
Picard Charles_Murison Picard
530
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
141
Ramasamy_N
Captain Ramasamy_N Captain
115
Mr_Peach
Mr_Peach
Cadet
Posted: ‎2023-12-19 03:44 AM
Anybody found a solution for the below? max pulse rate 20mS. Need longer pulse rate?
How does PM5100 Pulse output work and what is the maximum Pulse ON time?
How does PM5100 Pulse output work and what is the maximum pulse ON time?
_____________________________________________________________
PM5100
ION Setup
Power Monitoring
PLC and Automation
As mentioned in PM5100 series Electrical characteristics, the meter has a Pulse Width of 50% duty cycle >20 ms, however, it's been observed many times in PM5100 series that the duration of the output pulse is too short to be detected by PLC or other pulse counters gave electrical characteristics
user guide pulse width of 50% duty cycle >20 ms s not explained in the user guide, 1/2 of cycle ON and 1/2 of cycle OFF, indeed it provides only a short pulse either ON or OFF, depending if one has installed the resistor or not.
Solution
One proper resistor is needed to have the circuit be completely looped:
PM5000 digital outputs are voltage-based circuits and current will be fixed in the output (Example 24VDC/20mA with 1.2K pull-up resistor).
The current level is constant ( ON = 20mA Max and OFF = 0.03uA ). So the DO can meet the pulse trigger (>2.1mA) requirement.
Example If you are using a 24V power supply R= 24V/20mA = 1kohm (minimum)
Current should be limited to 20mA.
Please follow below wiring diagram for the DO connection.
The pulse ON time PM5110 digital output is fixed for 20mS and it can not be increased at present.
We are checking the feasibility of adding this pulse ON time as user configurable (50mS, 100mS) from the fixed 20mS.
Released for:Schneider Electric Egypt and North East Africa
Published on:4/11/2023Last Modified on:12/18/2023
Replies 0