I am trying to get data from the following flow meter.
and this is the modbus register list I was provided with.
I am getting values when I connected the flow meter directly to a USB to RS485 converter.
But when the flow meter is connected to my ES, I am not getting stable data.
What could be the cause for this?
All the data are in this link : FLOW METER ISSUE
Thank you for the reply!
However, the issue has been solved!
The issue was that the register I needed to read was in float 32bit type. I had to extract the register using 16bit points and bit masks as four different points and then write a script to merge those four extracted points into one float point.
Hello Vihanger,
For modbus serial communications, there could be a few things happening. On the RS-485 side of things, perhaps you need to bias the serial loop. Example https://commons.wikimedia.org/wiki/File:Rs485-bias-termination.svg.
From the modbus side, perhaps you are requesting data faster than the flow meter can handle.
Charles