Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Ask questions, get advice from experts and peers on Digital Automation & Energy Management.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-09 10:27 PM
I am trying to connect a Siemens Cerberus FC924 fire panel to a Schneider AS-P controller running firmware version 3.2 through BACnet IP. The panel is successfully online, and I can see the points, but they are presented as Life Safety Points instead of the expected Analog Inputs (AI) or Binary Inputs (BI).
The issue is that the AS-P does not seem to read any changes in these points. However, when I connected the fire panel to a computer and monitored the values through Yabe, it showed the value changes. I have added a screen record of Yabe and AS-P here.
Has anyone encountered a similar issue? Does the AS-P support Life Safety Points, or is there a workaround to map these points as standard AI/BI objects? Any advice or guidance would be greatly appreciated!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-24 01:06 AM
Dear Vihanger,
Currently the BACnet Life Safety objects aren't yet supported in EBO product lines.
See below link:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-12 10:26 PM
Are you try to renew subscriptions.
Yabe is polling. Try use COV. EBO use primally COV.
If COV is not working with Siemens then use this guide
BACnet blacklist implementation to disable features in an EBO Server BACnet interface. - Schneider E...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-24 01:06 AM
Dear Vihanger,
Currently the BACnet Life Safety objects aren't yet supported in EBO product lines.
See below link:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-29 04:15 AM
Thank you all for your replies. I had to use a separate gateway between the Fire Panel and the BMS to convert the Life Safety Points into BACnet digital points.
Link copied. Please paste this link to share this article on your social media post.