Issue with Reading Life Safety Points from Siemens Cerberus FC924 on AS-P (3.2) via BACnet IP

Ask the Community

Ask questions, get advice from experts and peers on Digital Automation & Energy Management.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Support
  • Ask the Community
  • Issue with Reading Life Safety Points from Siemens Cerberus FC924 on AS-P (3.2) via BACnet IP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
35
MikaelKrantz
Kirk MikaelKrantz Kirk
7
Omaelk
Janeway Omaelk
3
chris_clerc
Administrator chris_clerc Administrator
2
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Ask the Community
Start a Topic
Solved
vihanger
Crewman vihanger
Crewman

Posted: ‎2024-12-09 10:27 PM

0 Likes
3
683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-09 10:27 PM

Issue with Reading Life Safety Points from Siemens Cerberus FC924 on AS-P (3.2) via BACnet IP

I am trying to connect a Siemens Cerberus FC924 fire panel to a Schneider AS-P controller running firmware version 3.2 through BACnet IP. The panel is successfully online, and I can see the points, but they are presented as Life Safety Points instead of the expected Analog Inputs (AI) or Binary Inputs (BI).

 

The issue is that the AS-P does not seem to read any changes in these points. However, when I connected the fire panel to a computer and monitored the values through Yabe, it showed the value changes. I have added a screen record of Yabe and AS-P here.

Has anyone encountered a similar issue? Does the AS-P support Life Safety Points, or is there a workaround to map these points as standard AI/BI objects? Any advice or guidance would be greatly appreciated!

Labels
  • Labels:
  • Others & accessories
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Fendour
Lieutenant | EcoXpert Master Fendour Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-01-24 01:06 AM

1 Like
0
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-24 01:06 AM

Dear Vihanger,

 

Currently the BACnet Life Safety objects aren't yet supported in EBO product lines.

 

See below link:

https://community.se.com/t5/Building-Automation-Knowledge/Unable-to-see-Life-Safety-objects-from-Fir...

 

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
janim
Spock janim Spock
Spock

Posted: ‎2024-12-12 10:26 PM

1 Like
0
648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-12 10:26 PM

Are you try to renew subscriptions. 

Yabe is polling. Try use COV. EBO use primally COV.  

janim_0-1734071086792.png

If COV is not working with Siemens then use this guide
BACnet blacklist implementation to disable features in an EBO Server BACnet interface. - Schneider E...



If it ain't broke, don't fix it.
Reply

Link copied. Please paste this link to share this article on your social media post.

Fendour
Lieutenant | EcoXpert Master Fendour Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-01-24 01:06 AM

1 Like
0
629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-24 01:06 AM

Dear Vihanger,

 

Currently the BACnet Life Safety objects aren't yet supported in EBO product lines.

 

See below link:

https://community.se.com/t5/Building-Automation-Knowledge/Unable-to-see-Life-Safety-objects-from-Fir...

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

vihanger
Crewman vihanger
Crewman

Posted: ‎2025-09-29 04:15 AM

1 Like
0
70
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-29 04:15 AM

Thank you all for your replies. I had to use a separate gateway between the Fire Panel and the BMS to convert the Life Safety Points into BACnet digital points.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore