Posted: 2024-10-2910:16 AM
Device Administrator
When attempting to add a server to Device Administrator, window pops up saying could not find the server on "XX.XX.XX.XX (IP address)", however, WorkStation can log on to the server (AS-P), version 3.1.2.29
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-0403:04 PM. Last Modified: 2024-11-0403:05 PM
@BrianUSAF Device Administrator uses TCP port 22 to communicate with the Automation Servers while WorkStation uses TCP port 80. Check that TCP port 22 is open bi-directionally between the devices.