A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-12 12:19 PM
Our project uses AVEVA System Platform 2023 to communicate with a Schneider M580 controller.
We have successfully established communications using the MBTCP driver. However, we would prefer to use OPC/UA. Is it possible to communicate directly with the controller, or do we need a BMENUA0100 (or similar) in order to use OPC/UA?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-02 10:54 PM
Hello,
Yes, you need a BMENUA0100 Card due OPCUA Server. In the latest firmware versions, the OPCUA Client has been incorporated into the M580, but for your architecture you need the OPCUA Server offered by the NUA Card
Best regards
Ricard
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-03 08:33 PM
Hi @RayLonghurst,
I believe @Ricard is correct. If you want to use OPCUA Client from System Platform, you would need the BMENUA0100 Card, that hosts the OPCUA Server.
Another approach, could be to use OFS and the OPC OI Server (it is actually a OPC DA Client) in System Platform. This would not require any additional hardware and would take advantage of OFS ability to send 1024 bytes of data with each request (Modbus TCP is limited to 256 bytes).
Let us know which approach you end up on and how it performs for you.
Kind regards
Olivier
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-02 10:54 PM
Hello,
Yes, you need a BMENUA0100 Card due OPCUA Server. In the latest firmware versions, the OPCUA Client has been incorporated into the M580, but for your architecture you need the OPCUA Server offered by the NUA Card
Best regards
Ricard
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-03 08:33 PM
Hi @RayLonghurst,
I believe @Ricard is correct. If you want to use OPCUA Client from System Platform, you would need the BMENUA0100 Card, that hosts the OPCUA Server.
Another approach, could be to use OFS and the OPC OI Server (it is actually a OPC DA Client) in System Platform. This would not require any additional hardware and would take advantage of OFS ability to send 1024 bytes of data with each request (Modbus TCP is limited to 256 bytes).
Let us know which approach you end up on and how it performs for you.
Kind regards
Olivier
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 08:35 AM
Hi @olivier_vallee & @Ricard We are dealing with a SIL3 level M580 PAC and the SCADA used is Aveva Intouch (2023). We were Initially planning on using OPC UA as the communication protocol but I have came to know that Safety PLC doesn't support OPC UA. Could you share some insights?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 10:03 PM
Hello @amaljt
The M580 Safety is compatible with the BMENUA0100 communication card to be OPCUA Server.
BR
Ricard