waveform - picture request BX1500G

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • waveform - picture request BX1500G
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

0 Likes
4
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

waveform - picture request BX1500G

I would like to see an actual Oscilloscope output waveform picture of the Stepped approximation to a sinewave. If possible from the specific UPS that I am using.
BX1500G - Power Saving Back-UPS XS 1500
http://www.apcc.com/products/resource/include/techspec_index.cfm?base_sku=BX1500G&tab=models
Can someone from APC technical support please post a picture of the output at load for this model?
I tried to call technical support, but they told me to Google it, yeah ok that didn't work for my model.
I got general information about how it would work, but not how specifically my unit works.
If you would like to make more customers happy, how about posting this data directly on the technical specifications page in which the product appears? This would be especially nice on the "pure" sine wave versions as well so we can see what that's supposed to look like, instead of what the stepped looks like.
Yes I know what a ideal sine wave looks like, and that grid power doesn't always look that great, but compared to a square wave at least my PC doesn't power off when the power does. No I haven't had any trouble yet, but the tech in me wants to know and the penny pincher wants to get something good enough, but not bad. I figure if this UPS is sold with the "intention" of being used on a PC then it should work on my PC, otherwise they should not sell anything but Pure Sine wave UPSs if they are intended for PC use.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
  • smart-ups
  • waveforms
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

0 Likes
0
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

I would like to see an actual Oscilloscope output waveform picture of the Stepped approximation to a sinewave. If possible from the specific UPS that I am using.
BX1500G - Power Saving Back-UPS XS 1500
http://www.apcc.com/products/resource/include/techspec_index.cfm?base_sku=BX1500G&tab=models
Can someone from APC technical support please post a picture of the output at load for this model?
I tried to call technical support, but they told me to Google it, yeah ok that didn't work for my model.
I got general information about how it would work, but not how specifically my unit works.
If you would like to make more customers happy, how about posting this data directly on the technical specifications page in which the product appears? This would be especially nice on the "pure" sine wave versions as well so we can see what that's supposed to look like, instead of what the stepped looks like.
Yes I know what a ideal sine wave looks like, and that grid power doesn't always look that great, but compared to a square wave at least my PC doesn't power off when the power does. No I haven't had any trouble yet, but the tech in me wants to know and the penny pincher wants to get something good enough, but not bad. I figure if this UPS is sold with the "intention" of being used on a PC then it should work on my PC, otherwise they should not sell anything but Pure Sine wave UPSs if they are intended for PC use.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

0 Likes
0
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

Thanks for the waveforms Impedance. I see that for the most part it's a pure square wave not really stepped that much at all, it would have been nice if there was one more step in the sequence, but I guess that's what makes them less expensive, oh and yes I will be getting a pure sine wave version next, it's just a shame though that I can't just pick one up at my local Best Buy, they really shouldn't sell anything but pure sine wave any more with all the new power supplies running active PFCs.

Message was edited by: g3412

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

0 Likes
0
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

Unfortunately we do not have documentation depicting the actual sine wave shape of the UPS. If you would like to research about it the wave form is called Step Approximated or Quasi Sine Wave. Hope this helps.

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

0 Likes
0
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

OK so APC doesn't document the waveforms, but does someone else have this model (or generation model) and a oscilloscope, that would be willing to post a picture of the waveform under load (half power is fine, but full power is desirable)
Note to APC, for the future, could you consider documenting this for your tech minded customers please!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

0 Likes
0
1090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:35 AM . Last Modified: ‎2024-03-22 01:21 AM

I would like to see an actual Oscilloscope output waveform picture of the Stepped approximation to a sinewave. If possible from the specific UPS that I am using.
BX1500G - Power Saving Back-UPS XS 1500
http://www.apcc.com/products/resource/include/techspec_index.cfm?base_sku=BX1500G&tab=models
Can someone from APC technical support please post a picture of the output at load for this model?
I tried to call technical support, but they told me to Google it, yeah ok that didn't work for my model.
I got general information about how it would work, but not how specifically my unit works.
If you would like to make more customers happy, how about posting this data directly on the technical specifications page in which the product appears? This would be especially nice on the "pure" sine wave versions as well so we can see what that's supposed to look like, instead of what the stepped looks like.
Yes I know what a ideal sine wave looks like, and that grid power doesn't always look that great, but compared to a square wave at least my PC doesn't power off when the power does. No I haven't had any trouble yet, but the tech in me wants to know and the penny pincher wants to get something good enough, but not bad. I figure if this UPS is sold with the "intention" of being used on a PC then it should work on my PC, otherwise they should not sell anything but Pure Sine wave UPSs if they are intended for PC use.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore