restart NAS after power outage

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • restart NAS after power outage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
6
4073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

restart NAS after power outage

Hi,
I yesterday received my Back UPS BR550GI.
Attached to my NAS its operating fine and shutting down when a 50% battery level is reached.

Now my question: How can I restart my NAS, once power is re-established?
I thought the UPS will disconnect the device and then reconnect to enable boot.

If I manually disconnect my NAS from UPS and then reconnect it, the NAS will boot up.

Could you help me to achieve an automatic restart after power failure shutdown?

Thanks,
Wolfram

Message was edited by: wopl

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
0
4067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

right, i understand that PCPE is not running on the NAS. none of the timers are adjustable via PCPE.

i can think of one decent way - look into the BH500NET UPS which allows someone on the same subnet cycle the power to outlets remotely. you shouldnt have to physically walk over to the UPS to do this but would need to login to the BH500NET.

i cant think of an automated way of doing this on any UPS if the UPS does not enter sleep mode at any point. unfortunately, PCPE needs to be running to control the UPS to shutdown and use the preserve battery power setting.

you can get into more expensive solutions with switched rack PDUs to control outlets and maybe bigger UPSs with other work arounds but they all work the same way - the UPS must cycle power to the outlets and to do that, it needs to go to sleep mode first.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
0
4067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

Not sure about your remark and questions...

Sure, the UPS continues to work on batteries (what else?) until power comes back... basically without any load
What LED's? What Beeps?

Wolfram

Message was edited by: wopl

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
0
4067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

o.k., no probs...
yep, battery icon remains and 4-beeps continues (after UPS-caused shutdown of NAS).

When power comes back, UPS goes from battery to power state.
NAS does not boot - which I would like it to do.

NAS currently is a Thecus N5200 (will be replaced very soon)
Wolfram

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
0
4068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

if the UPS never goes to sleep - whether told to by software or whether it runs out of battery power, then I don't think this will work. the UPS needs to reboot itself, thus rebooting the NAS, to force the NAS back on. the UPS is telling the NAS to go to sleep at 50% battery power remaining but then if the power comes back on before the UPS goes to sleep but after the NAS shuts down, so lets say at 40% battery power left, the UPS does not turn off since utility power (it comes back online and never shuts down). this is the same issue with a server or any other type of device. the only way to get it to turn back on is manually, as you've found out. the UPS needs to go to sleep mode to tell the outlets to reboot and thus start the NAS back up.

here is some more info on how things work..

Shutdown time line, software not installed:

1. UPS goes to battery, the on battery beep sounds

2. The UPS will sound the on battery beep until it reaches the last few minutes of run time. The length of time depends on the load and how old the battery is.

3. When the unit reaches the last few minutes of battery life it will then sound its low battery alarm.

4. Just before the battery is completely exhausted the ups will turn itself off.

5. If the UPS went to battery due to a brown out the unit at this point will be in LVSM until the voltage becomes acceptable again.

PowerChute Personal Edition default shutdown time line:

1. UPS goes to battery and PCPE starts its preserve battery power counter.

2. When the counter expires it sends a command to the UPS to start counting its turn off delay and then commands the OS to shutdown.

3. The operating system shuts down and the UPS continues to count its turn off delay. (Once the UPS finishes counting its turn off delay it will reboot and nothing can stop this from happening.)

4. The UPS cuts power to the outlets then rechecks to see if the incoming power is acceptable. If it is not it waits there until power returns.

5. If the UPS went to battery due to a brown out the unit at this point will be in LVSM until the voltage becomes acceptable again.


hope this helps..you may be able to edit some settings using the software with a computer and then disconnect the computer if you don't want it attached all the time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
0
4069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

o.k., this is much more complicated than expected
On my NAS PCPE is not running. I have a module that reads all APC values and shuts down my NAS based on battery-percentage or minutes of battery operation. Shutdown of NAS works reliably and well.

As there is no load, it will take hours until UPS will shut down (until battery is discharged). If during this time power is back again, the NAS (and UPS) will never restart.
I also prefer the battery-preserve mode... so shutting down my NAS at a whatever % of battery (or maybe minutes of battery operation).

UPS should see (threshold), that my NAS (master outlet) was shut down by going into battery mode.
Or there should be a timer within the UPS (timeout after NAS starting to go down), which I cannot find in my PCPE software.
Once power is re-established UPS "just" needs to disconnect power outlets (well, or basically reboot itself).

Sure, that this function is not available the way I need it?
This means there is no reliable way to start up my NAS again.
Would such function be supported by more expensive APC units?

Thanks for your help.
Wolfram

Message was edited by: wopl

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
0
4068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

right, i understand that PCPE is not running on the NAS. none of the timers are adjustable via PCPE.

i can think of one decent way - look into the BH500NET UPS which allows someone on the same subnet cycle the power to outlets remotely. you shouldnt have to physically walk over to the UPS to do this but would need to login to the BH500NET.

i cant think of an automated way of doing this on any UPS if the UPS does not enter sleep mode at any point. unfortunately, PCPE needs to be running to control the UPS to shutdown and use the preserve battery power setting.

you can get into more expensive solutions with switched rack PDUs to control outlets and maybe bigger UPSs with other work arounds but they all work the same way - the UPS must cycle power to the outlets and to do that, it needs to go to sleep mode first.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

0 Likes
0
4069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:38 AM . Last Modified: ‎2024-03-22 01:19 AM

Hi,
I yesterday received my Back UPS BR550GI.
Attached to my NAS its operating fine and shutting down when a 50% battery level is reached.

Now my question: How can I restart my NAS, once power is re-established?
I thought the UPS will disconnect the device and then reconnect to enable boot.

If I manually disconnect my NAS from UPS and then reconnect it, the NAS will boot up.

Could you help me to achieve an automatic restart after power failure shutdown?

Thanks,
Wolfram

Message was edited by: wopl

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore