Posted: 2025-05-26 03:06 PM
I've just noticed that my APC Back-UPS Pro 1600 does not seem to have "Runtime calibration" option anywhere.
In the "PowerChute Serial Shutdown" (PowerChute Serial Shutdown Agent Version 1.3.0.301),
the "Select diagnostic action" drop-down menu only provides "None selected", "Self Test", "Test Alarm" options.
The built-in help ( https://localhost:6547/help/english/BackUPS/index.html#page/PCSS_UserGuide%2FDeviceModel.html ) explicitly says that only these two option are available:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-27 04:08 AM
The Back-UPS Series was supported by PCPE not PCBE. You may try the last version of PCPE to see if the battery calibration is present.
If it’s not than obviously PCSS would not support the same. You may contact APC Technical Support to obtain the last copy of PCPE if available.
Otherwise, you’ll need to find a copy you trust to download.
Another option is to use third party software like APCUPSD / NUT to invoke the battery calibration if present.
Lastly, a battery calibration should only be performed when the cartridge has been replaced or when the expected runtime displayed is wildly off.
As invoking the battery calibration impacts the 260 cycle life which affects and shortens the service life of the cell.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-03 03:02 AM
Please refer to this post for how to run a manual runtime calibration on your Back-UPS. A software-initiated runtime calibration for Back-UPS is not supported in PowerChute Serial Shutdown and also not in the older PowerChute Personal Edition software. Most modern Back-UPS do seem to support the runtime calibration USB HID usage. Thus support for runtime calibration for Back-UPS may be added in a future PowerChute Serial Shutdown release. The typos in the on-line help will be addressed in next release.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-07 07:44 AM
@Teken ,
@fredkm ,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-09 06:47 AM
At a high level in a enterprise environment all of the batteries are replaced on a scheduled interval based on each sites unique conditions such as power quality, usage, environmental, and mission critical status.
The average service life of the batteries are 2-5 years based on usage, temperature, and environmental conditions.
The vast majority of stringent ISO sites replace the RBC at the three year interval. While others are replaced at the maximum of four year interval regardless of any pass / fail tests conducted.
The APC Self Test is a very crude method to get an idea of the RBC health. It in no way is a true indicator of the RBC health or operational runtime of the cartridge.
A yearly lights out / grid down validation test is one of the major benchmarks & indicators when compared to the APC Runtime Calculator as to battery health.
This is coupled by measuring every cell for internal resistance and comparing it to the manufacturers stated specifications / data sheet.
Other validation tests are at rest voltage readings after being fully charged and what the values are after 24 ~ 72 hours. Along with carbon pile load testing at a defined wattage for a duration called out by the manufacturers data sheet.
All RBC / individual cells are monitored by a thermal imaging camera to record expected temperature rise or out of band elevated internal temperatures.
All of the above insures the RBC is providing the expected performance and operational runtime needed for the infrastructure.
A battery calibration is only required upon a RBC being replaced or (IF) the displayed / calculated runtime is wildly off.
As noted earlier an annual lights out / grid down validation test is the equivalent to a battery calibration. Both are extremely stressful on the RBC and goes against the 260 cycle life of the cells. ☝️