Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Apc selection and inrush current
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-0906:16 AM
If this message / indicator is showing this means there’s a problem with the connected load. More than likely the unit is simply overloaded and thus shutting down.
You can test this theory by simply replacing the load with something else and see how the unit behaves and report back the results.
Generally speaking a UPS should only be loaded up to 80% of it’s rated capacity. A 700 RMS load should have at least 1000 ~ 1500 VA UPS at the lower tier.
A 2000 VA is more appropriate in terms of capacity, headroom, and operational runtime to complete a graceful shutdown.