I have a backups xs1000 and I noticed today there was the following message:
EpPG0f7Nsy6r%2FPJ5qtReYQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Does this mean I have to get a new battery or replace the whole unit? I need to act quick so please respond quick, thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
yeah i had a rep respond via support tickets. was out of warantee but they did offer trade ups discount.
ns1080g is the new unit i purchased to replace it with for now..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
Normally, for the fastest response, you should contact APC Technical Support via phone. The numbers for various countries can be found here. However, that support is Monday-Friday 8AM-8PM Eastern Time in the US. So an APC person may see your post here and answer it before Monday.
I don't use PowerChute (my units all have network management cards), but there is probably some sort of event log available. That might be in the "Technical Data" or "Current Status" on the left side of the screenshot you posted. Information may also be available on the unit's front panel, either LEDs and/or LCD display. If you could post all of that info here, that will help anyone familiar with your UPS model to give you advice.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
I went and bought a replacement for now but I need that other one fixed still. I submitted a support request last night and will be giving them a call monday.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
Liz,
Sorry for the delay in responding. I had to research the error. I have a few questions, is this device BX1000G? If yes, what's message on the LCD screen and buzzer at that time? Can the UPS still provide output power when PCPE shows this alarm? I assume it happened during or just after a self-test ran? This dialog should be thrown when a Self test fails because of the charger module failure.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
Yes it is a BX1000G. it was an F06 error. It shuts everything off.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
Hi,
F06 indicates a Relay Weld which means one of the relays is in a locked/stuck position and is not functioning properly. You did the right thing replacing the unit. If the unit is less 2 years old you can contact Technical Support for a replacement. In the U.S. the number is 800-890-4272.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:55 PM . Last Modified: 2024-03-19 11:47 PM
yeah i had a rep respond via support tickets. was out of warantee but they did offer trade ups discount.
ns1080g is the new unit i purchased to replace it with for now..