Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

beeping Back-UPS Pro 1000

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • beeping Back-UPS Pro 1000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
104
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:29 AM . Last Modified: ‎2024-03-27 12:57 AM

0 Likes
0
555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:29 AM . Last Modified: ‎2024-03-27 12:57 AM

beeping Back-UPS Pro 1000

We have a Back-UPS Pro 1000 with one server, a NAS, a switch, a KVM, and a monitor on it.  The load on the UPS says around 400 W.  The UPS is rated at 600 W.  We get (usually in the evening) beeps from the UPS.  One day an employee (whose office is just across from the room where this is) said that it beeped at 6:05, 7:05, 8:05, and 9:05.  We thought it might be the power coming into the UPS.  We had the building management people check the power and everything seems fine.  The room where it is was supposed to have it's own circuit.  However, we found that another office (shipping) is also on the circuit.  We are going to correct that.  We happened to have another UPS (same model), so I put the server on it and left everything else on the other one.  I also added a desktop computer to the second UPS.  So, there is 200 W on each UPS.  That solved the beeping problem.  We had a power outage and the server powered off as soon as the UPS went into battery mode.  Kind of defeats the purpose.  I understand that when the UPS is in battery mode, it isn't providing 120 V - more like 90-100 V.  Is it possible that the server won't run on 90-100 V?  This is a development setup.  The main rack is on a Smart-UPS X (SMX3000RMLV2UNC) with 2 auxiliary batteries.  It showed 120 V for the output voltage during the time it was in battery mode.  It has 7 servers, 2 NASs, and about a dozen misc. network hardware on it.  The UPS shows about 1900 W load.  It lasted an hour on battery and everything stayed up.

What's wrong with the Back-UPS Pro 1000?  Why can't we get closer to the 600 W of capacity?

Is there a product in that load range that will give us a full 120 V while on battery?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • beeping
  • capacity
  • low
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of