back-ups 675 constant tone and yellow light when gaming pc is playing intensive games plugged into battery+surge slot only

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • back-ups 675 constant tone and yellow light when gaming pc is playing intensive games plugged into battery+surge slot only
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2022-10-29 05:47 PM . Last Modified: ‎2022-10-29 05:53 PM

0 Likes
3
12137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-29 05:47 PM . Last Modified: ‎2022-10-29 05:53 PM

back-ups 675 constant tone and yellow light when gaming pc is playing intensive games plugged into battery+surge slot only

I inherited a Back-UPS 675 from my dad who passed recently, he seems to have bought this UPS back in 2020.  I had it shipped cross country to me from a friend and I forgot to tell him to disconnect the battery inside but everything seems to be working fine despite this.

 

The problem I have is when I plug in my gaming PC (850W Corsair PSU running a 3070 Ti and Ryzen 7 5800X CPU) it is okay in the Surge only slot, but when I plug it into the Battery+Surge slot and then run games, during some specific gaming scenes the UPS will turn on a loud constant beeping tone and the green led power button will change to an amber/yellow led color.  It will be constant until I leave the game scene (sometimes a menu, sometimes a 3d area, depends on the game), at which point it returns to green and the tone stops.

 

So at this point I can only plug my PC into the Surge only outlet when using my PC, but I know my dad's PC had a 2070 Super GPU and a Ryzen 3800X CPU and mine doesn't draw that much higher of power.  I know he used his PC in the battery+surge slot in case of black outs down in Puerto Rico so I am curious why his PC didn't have this issue with this UPS but mine does.

 

Am I doing something wrong?  I have tried the 3 different power fluctuation level settings in the instructions I found online, green, amber, or red, but it does the same thing with all 3 settings.  Is there anything that can be done or is my PC just too power hungry for this Back-UPS 675, or is the battery too old?  Any ideas could be helpful.  It does have a USB Data outlet on the back but I don't have that cable so it is not plugged in.

 

As a side note I have looked at this web page https://www.apc.com/us/en/faqs/FA158810/ but the difference is when I get this constant tone the led is not flashing, it is a constant yellow/amber color.

 

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
RMZahn
Crewman RMZahn
Crewman

Posted: ‎2022-11-04 02:27 AM

0 Likes
2
12039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-04 02:27 AM

as I read, this UPS delivers max 360W - so its too weak for your PC - especially if you demand higher power playing games 😉

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-11-04 11:14 PM

In response to RMZahn
0 Likes
1
12029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-04 11:14 PM

What model would you recommend that would work for a 3070 Ti and 5800X CPU with a 850W Corsair 80 Plus Gold PSU?

 

Since my dad had a 2070 Super plus a 3800X CPU, I assume it must still work for his so I could plug my PC into the Surge only port and then plug his into the Battery+Surge port (if I can find the space to set up both PC's in this room).

 

And is there an easy way to get a replacement battery when it inevitably dies?  I think it has been around 2 years since he bought it so I have a feeling it will need one at some point.

 

Luckily here we don't have many surge events or rolling blackouts so I have never needed a UPS in the past, but they are good insurance "in case".  Though I guess if a normal surge protecting power bar (can't say the other word) is good enough too I have been using several of those.

Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-07 04:21 AM

In response to Anonymous user
0 Likes
0
12016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 04:21 AM

Hi @Anonymous user,

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  Apologies for the issue that you are having, I agree with @RMZahn that your UPS is somehow exhibiting an overload condition.

 

If you can, I suggest that you reach out to our team that handles your country for proper guidance in finding an authorized UPS and battery reseller.

 

https://www.se.com/ww/en/work/support/country-selector/contact-us.jsp 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore