apc powerchute software: not able to test the UPS and events are not registered

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • apc powerchute software: not able to test the UPS and events are not registered
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-26 10:37 PM

0 Likes
8
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-26 10:37 PM

apc powerchute software: not able to test the UPS and events are not registered

hello everybody, i need your help urgently; 

i have an APC Back-up UPS, i use APC powerchute 3 software on my pc, however it is not able to run a test about the battery's state. it just says it can't. and more,  blackouts and general events are not registered in the event list. 

why this? it is connected to the ups through cable, should i plug the ethernet cable also?

please help me, i'm confused

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

Hi,

The screenshot shows the software is getting model and serial number information for the Back-UPS. It should get on battery data as well and be able to run a self-test assuming communications is not disrupted. Do you have another PC you could temporarily connect to the UPS with PowerChute to test to see if it experience the same issue? 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-26 10:37 PM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-26 10:37 PM

Hi,

A Back-UPS is compatible with PowerChute Personal Edition. Would you please send screenshots of the Current Status and of the Technical Data pages. Also, please provide a screenshot of Control panel - Device manager - Batteries. See Schneider Electric FAQ FA310907

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-26 10:37 PM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-26 10:37 PM

hello bill, here are the informations you requested me;

what i can't do: the software is not able to run an automatic test. also, the black-out event that i had yesterday has not been registered into the event list (as you can see, it shows 0 in the last 4 weeks); is there anything i'm doing wrong? like, i should run the software while the Back-UPS is running?

ps. it's the powerchute personal edition, as you said

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

Hi,

The software is showing there is no load on the UPS. Also you did not send a screenshot of the dati tecnic page.

There may be an issue with communications and that would explain why the software does on report outages.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

so what should i do?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

may i have any answer?  Bill  Secret  Bill what is the purpose of this forum if you don't reply?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

deeee,

Sorry. I have been on holiday.

On 8/16/2018 5:49 AM, deeee said:

what is the purpose of this forum if you don't reply?

The purpose of the forum is for user to assist other users and share ideas. Yes, people such as myself that work for Schneider Electric do moderate the forum and we assist users with their questions. However when you need immediate assistance from Schneider Electric you should contact local Technical Support.

I asked for a screen shot of the technical data page. Would you please provide that. I will help me understand what data the software is receiving from the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

here it is.

i want to know why the software can't run the manual self-test "impossible to run self-test"

and why it doesn't either register past black-outs.

thanks.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

0 Likes
0
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:17 AM . Last Modified: ‎2024-03-26 10:36 PM

Hi,

The screenshot shows the software is getting model and serial number information for the Back-UPS. It should get on battery data as well and be able to run a self-test assuming communications is not disrupted. Do you have another PC you could temporarily connect to the UPS with PowerChute to test to see if it experience the same issue? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of