Posted: 2021-06-29 08:46 PM . Last Modified: 2024-03-21 12:34 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:46 PM . Last Modified: 2024-03-21 12:34 AM
Periodically, I will get a sudden loss of power to my desk area only (not the whole house) and my UPS doesn't switch to battery. The log just says: Are some the receptacles unswitchable, or could my settings be causing this?
2/4/10 22:44:41 Communication Established
2/4/10 22:44:30 Monitoring Started
2/1/10 16:19:10 Communication Established
2/1/10 16:18:48 Monitoring Started
1/31/10 22:24:37 Communication Established
1/31/10 22:24:22 Monitoring Started
1/31/10 06:23:48 Communication Established
1/31/10 06:23:41 Monitoring Started
1/31/10 06:21:12 Monitoring Stopped
1/28/10 22:24:40 Communication Established
1/28/10 22:24:33 Monitoring Started
1/26/10 03:19:06 Communication Established
1/26/10 03:18:59 Monitoring Started
1/26/10 03:16:38 Monitoring Stopped
1/18/10 18:39:22 Communication Established
1/18/10 18:39:15 Monitoring Started
1/13/10 22:59:12 Battery Needs Replacing
I don't know why it said bettery needs replacing that one time, becasue all is well now:
UPS System Parameters Status
Device Status On line
UPS Load 28.0 %
Runtime Remaining 45 Minutes
Internal Temperature 35.1 °C / 95.2 °F
Power Status
Line Voltage 117.6 VAC
Output Voltage 117.6 VAC
Output Frequency 60.0 Hz
Battery Status
Battery Charge 100.0 %
Battery Voltage 27.9 VDC
2/5/10 20:44:58 118.3 119.6 118.9 118.9 60.00 27.87 27.0 35.1
2/5/10 20:24:59 118.3 119.6 118.9 119.6 60.00 27.87 27.0 35.1
2/5/10 20:04:59 117.0 118.3 117.6 117.6 60.00 27.87 28.0 35.1
2/5/10 19:44:59 118.3 119.6 118.9 118.9 60.00 27.87 27.0 35.5
2/5/10 19:24:59 118.9 120.2 119.6 119.6 60.00 27.87 27.0 35.5
2/5/10 19:04:59 118.9 120.2 119.6 119.6 60.00 27.87 22.3 35.5
2/5/10 18:44:59 119.6 120.2 120.2 120.2 60.00 27.87 27.0 35.5
2/5/10 18:24:59 120.2 121.5 120.9 120.9 60.00 27.87 28.6 35.5
2/5/10 18:04:59 119.6 120.2 120.2 120.2 60.00 27.87 28.0 35.5
2/5/10 17:44:59 118.9 120.2 119.6 119.6 60.00 27.87 27.0 35.5
2/5/10 17:24:59 118.3 120.2 118.9 118.9 60.00 27.87 27.0 35.5
2/5/10 17:04:59 118.9 120.2 120.2 120.2 60.00 27.87 26.5 35.5
2/5/10 16:44:59 119.6 120.2 120.2 120.2 60.00 27.87 26.5 35.1
2/5/10 16:24:59 120.2 120.9 120.9 120.9 60.00 27.87 27.0 35.1
2/5/10 16:04:59 118.9 120.2 119.6 119.6 60.00 27.87 27.0 35.1
2/5/10 15:44:59 119.6 120.2 120.2 120.2 60.00 27.87 28.0 35.1
2/5/10 15:25:00 119.6 120.2 120.2 120.2 60.00 27.87 21.8 35.1
2/5/10 15:05:00 120.2 120.9 120.2 120.9 60.00 27.87 27.0 35.1
2/5/10 14:45:00 120.9 122.2 122.2 122.2 60.00 27.87 27.0 35.1
2/5/10 14:25:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 35.1
2/5/10 14:05:00 121.5 122.2 122.2 122.2 60.00 27.87 21.8 35.1
2/5/10 13:45:00 120.9 122.2 121.5 121.5 60.00 27.87 21.8 35.1
2/5/10 13:25:00 120.2 121.5 121.5 121.5 60.00 27.87 21.8 35.1
2/5/10 13:05:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 35.1
2/5/10 12:45:00 120.2 120.9 120.2 120.2 60.00 27.87 22.3 35.1
2/5/10 12:25:00 120.2 121.5 120.9 120.9 60.00 27.87 22.3 35.1
2/5/10 12:05:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 35.1
2/5/10 11:45:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 34.6
2/5/10 11:25:00 120.2 121.5 121.5 121.5 60.00 27.87 22.3 35.1
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:46 PM . Last Modified: 2024-03-21 12:33 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:46 PM . Last Modified: 2024-03-21 12:33 AM
Periodically, I will get a sudden loss of power to my desk area only (not the whole house) and my UPS doesn't switch to battery. The log just says: Are some the receptacles unswitchable, or could my settings be causing this?
2/4/10 22:44:41 Communication Established
2/4/10 22:44:30 Monitoring Started
2/1/10 16:19:10 Communication Established
2/1/10 16:18:48 Monitoring Started
1/31/10 22:24:37 Communication Established
1/31/10 22:24:22 Monitoring Started
1/31/10 06:23:48 Communication Established
1/31/10 06:23:41 Monitoring Started
1/31/10 06:21:12 Monitoring Stopped
1/28/10 22:24:40 Communication Established
1/28/10 22:24:33 Monitoring Started
1/26/10 03:19:06 Communication Established
1/26/10 03:18:59 Monitoring Started
1/26/10 03:16:38 Monitoring Stopped
1/18/10 18:39:22 Communication Established
1/18/10 18:39:15 Monitoring Started
1/13/10 22:59:12 Battery Needs Replacing
I don't know why it said bettery needs replacing that one time, becasue all is well now:
UPS System Parameters Status
Device Status On line
UPS Load 28.0 %
Runtime Remaining 45 Minutes
Internal Temperature 35.1 °C / 95.2 °F
Power Status
Line Voltage 117.6 VAC
Output Voltage 117.6 VAC
Output Frequency 60.0 Hz
Battery Status
Battery Charge 100.0 %
Battery Voltage 27.9 VDC
2/5/10 20:44:58 118.3 119.6 118.9 118.9 60.00 27.87 27.0 35.1
2/5/10 20:24:59 118.3 119.6 118.9 119.6 60.00 27.87 27.0 35.1
2/5/10 20:04:59 117.0 118.3 117.6 117.6 60.00 27.87 28.0 35.1
2/5/10 19:44:59 118.3 119.6 118.9 118.9 60.00 27.87 27.0 35.5
2/5/10 19:24:59 118.9 120.2 119.6 119.6 60.00 27.87 27.0 35.5
2/5/10 19:04:59 118.9 120.2 119.6 119.6 60.00 27.87 22.3 35.5
2/5/10 18:44:59 119.6 120.2 120.2 120.2 60.00 27.87 27.0 35.5
2/5/10 18:24:59 120.2 121.5 120.9 120.9 60.00 27.87 28.6 35.5
2/5/10 18:04:59 119.6 120.2 120.2 120.2 60.00 27.87 28.0 35.5
2/5/10 17:44:59 118.9 120.2 119.6 119.6 60.00 27.87 27.0 35.5
2/5/10 17:24:59 118.3 120.2 118.9 118.9 60.00 27.87 27.0 35.5
2/5/10 17:04:59 118.9 120.2 120.2 120.2 60.00 27.87 26.5 35.5
2/5/10 16:44:59 119.6 120.2 120.2 120.2 60.00 27.87 26.5 35.1
2/5/10 16:24:59 120.2 120.9 120.9 120.9 60.00 27.87 27.0 35.1
2/5/10 16:04:59 118.9 120.2 119.6 119.6 60.00 27.87 27.0 35.1
2/5/10 15:44:59 119.6 120.2 120.2 120.2 60.00 27.87 28.0 35.1
2/5/10 15:25:00 119.6 120.2 120.2 120.2 60.00 27.87 21.8 35.1
2/5/10 15:05:00 120.2 120.9 120.2 120.9 60.00 27.87 27.0 35.1
2/5/10 14:45:00 120.9 122.2 122.2 122.2 60.00 27.87 27.0 35.1
2/5/10 14:25:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 35.1
2/5/10 14:05:00 121.5 122.2 122.2 122.2 60.00 27.87 21.8 35.1
2/5/10 13:45:00 120.9 122.2 121.5 121.5 60.00 27.87 21.8 35.1
2/5/10 13:25:00 120.2 121.5 121.5 121.5 60.00 27.87 21.8 35.1
2/5/10 13:05:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 35.1
2/5/10 12:45:00 120.2 120.9 120.2 120.2 60.00 27.87 22.3 35.1
2/5/10 12:25:00 120.2 121.5 120.9 120.9 60.00 27.87 22.3 35.1
2/5/10 12:05:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 35.1
2/5/10 11:45:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 34.6
2/5/10 11:25:00 120.2 121.5 121.5 121.5 60.00 27.87 22.3 35.1
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:46 PM . Last Modified: 2024-03-21 12:33 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:46 PM . Last Modified: 2024-03-21 12:33 AM
The "change battery" detection is highly unreliable at best and usually fails to identify battery in need of replacing. It could also give a false positive if the UPS is overloaded.
First try a self-test with no load. If it passes, the inverter should be fine.
Then,
Run a UPS on 300 or 500W halogen light and try to make it go on battery and initiate a self-test by holding the button on the front for 3 seconds or so. If it responds by "replace battery" or 'overload' light or it shuts off, your batteries need replacing. You'll need two 12v 12Ah or 12120 batteries and save the fuse from the original battery. Batteries should cost $50-60 online.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:46 PM . Last Modified: 2024-03-21 12:33 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:46 PM . Last Modified: 2024-03-21 12:33 AM
Periodically, I will get a sudden loss of power to my desk area only (not the whole house) and my UPS doesn't switch to battery. The log just says: Are some the receptacles unswitchable, or could my settings be causing this?
2/4/10 22:44:41 Communication Established
2/4/10 22:44:30 Monitoring Started
2/1/10 16:19:10 Communication Established
2/1/10 16:18:48 Monitoring Started
1/31/10 22:24:37 Communication Established
1/31/10 22:24:22 Monitoring Started
1/31/10 06:23:48 Communication Established
1/31/10 06:23:41 Monitoring Started
1/31/10 06:21:12 Monitoring Stopped
1/28/10 22:24:40 Communication Established
1/28/10 22:24:33 Monitoring Started
1/26/10 03:19:06 Communication Established
1/26/10 03:18:59 Monitoring Started
1/26/10 03:16:38 Monitoring Stopped
1/18/10 18:39:22 Communication Established
1/18/10 18:39:15 Monitoring Started
1/13/10 22:59:12 Battery Needs Replacing
I don't know why it said bettery needs replacing that one time, becasue all is well now:
UPS System Parameters Status
Device Status On line
UPS Load 28.0 %
Runtime Remaining 45 Minutes
Internal Temperature 35.1 °C / 95.2 °F
Power Status
Line Voltage 117.6 VAC
Output Voltage 117.6 VAC
Output Frequency 60.0 Hz
Battery Status
Battery Charge 100.0 %
Battery Voltage 27.9 VDC
2/5/10 20:44:58 118.3 119.6 118.9 118.9 60.00 27.87 27.0 35.1
2/5/10 20:24:59 118.3 119.6 118.9 119.6 60.00 27.87 27.0 35.1
2/5/10 20:04:59 117.0 118.3 117.6 117.6 60.00 27.87 28.0 35.1
2/5/10 19:44:59 118.3 119.6 118.9 118.9 60.00 27.87 27.0 35.5
2/5/10 19:24:59 118.9 120.2 119.6 119.6 60.00 27.87 27.0 35.5
2/5/10 19:04:59 118.9 120.2 119.6 119.6 60.00 27.87 22.3 35.5
2/5/10 18:44:59 119.6 120.2 120.2 120.2 60.00 27.87 27.0 35.5
2/5/10 18:24:59 120.2 121.5 120.9 120.9 60.00 27.87 28.6 35.5
2/5/10 18:04:59 119.6 120.2 120.2 120.2 60.00 27.87 28.0 35.5
2/5/10 17:44:59 118.9 120.2 119.6 119.6 60.00 27.87 27.0 35.5
2/5/10 17:24:59 118.3 120.2 118.9 118.9 60.00 27.87 27.0 35.5
2/5/10 17:04:59 118.9 120.2 120.2 120.2 60.00 27.87 26.5 35.5
2/5/10 16:44:59 119.6 120.2 120.2 120.2 60.00 27.87 26.5 35.1
2/5/10 16:24:59 120.2 120.9 120.9 120.9 60.00 27.87 27.0 35.1
2/5/10 16:04:59 118.9 120.2 119.6 119.6 60.00 27.87 27.0 35.1
2/5/10 15:44:59 119.6 120.2 120.2 120.2 60.00 27.87 28.0 35.1
2/5/10 15:25:00 119.6 120.2 120.2 120.2 60.00 27.87 21.8 35.1
2/5/10 15:05:00 120.2 120.9 120.2 120.9 60.00 27.87 27.0 35.1
2/5/10 14:45:00 120.9 122.2 122.2 122.2 60.00 27.87 27.0 35.1
2/5/10 14:25:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 35.1
2/5/10 14:05:00 121.5 122.2 122.2 122.2 60.00 27.87 21.8 35.1
2/5/10 13:45:00 120.9 122.2 121.5 121.5 60.00 27.87 21.8 35.1
2/5/10 13:25:00 120.2 121.5 121.5 121.5 60.00 27.87 21.8 35.1
2/5/10 13:05:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 35.1
2/5/10 12:45:00 120.2 120.9 120.2 120.2 60.00 27.87 22.3 35.1
2/5/10 12:25:00 120.2 121.5 120.9 120.9 60.00 27.87 22.3 35.1
2/5/10 12:05:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 35.1
2/5/10 11:45:00 120.2 121.5 120.9 120.9 60.00 27.87 21.8 34.6
2/5/10 11:25:00 120.2 121.5 121.5 121.5 60.00 27.87 22.3 35.1
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of