Why does my Back-UPS XS1200CN not switch to AC power

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Why does my Back-UPS XS1200CN not switch to AC power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
HarryP
Crewman HarryP
Crewman

Posted: ‎2024-10-08 07:29 PM

0 Likes
7
1475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-08 07:29 PM

Why does my Back-UPS XS1200CN not switch to AC power

I've had an APC Back-UPS XS 1200 for about 12 years and have replaced the battery three times as needed. My last RBC32 battery was installed in late 2023 or early 2024 (the date on the slip that came with the replacement battery is 11/3/2023). I used your shipping instructions to ship the old battery to recycling around 04/22/2024 so I did the battery replacement close to the beginning of 2024 or end of 2023.

Today, my ups started giving four beeps every 30 seconds and refuses to switch to AC power. Any idea what I need to do to fix this? This ups is being used to supply power to my entertainment system (a/v, TV, cable box etc.) and is not normally connected to a PC; I have a second more current ups that I use for my computer. I ran the data cable to the XS1200 to see what it was reporting and it looks OK to me other than the fact it won't switch off battery to AC power. I tried pressing the fuse reset button as well as plugging it into different outlets to no effect. I tried reducing the sensitivity from MEDIUM to LOW but that also made no difference. By this point I don't have any devices plugged into any of the outlets on the back of the ups. The PowerChute utility reports the battery is at 50% charge but I don't think it is charging when plugged into the wall.

So, why won't it switch to AC power but remains on battery power? Is the relatively new battery defective?

The firmware level is 8.g1.DD.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-15 02:19 AM . Last Modified: ‎2024-10-15 02:19 AM

In response to HarryP
0 Likes
1
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-15 02:19 AM . Last Modified: ‎2024-10-15 02:19 AM

Given your unit is 12 years old it would make little sense in repairing the system.


If this is something you’re interested in doing any electronic repair shop can repair the unit.


You’ll need to balance the cost vs value in doing so as the APC FAQ as provided here notes the service life of their hardware is 7-10 years depending upon model.

 

This is where the hardware should be considered for a replacement or what the industry calls a hardware refresh. 👍

 

https://www.apc.com/ca/en/faqs/FAQ000265093/

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-09 06:02 AM

0 Likes
6
1474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-09 06:02 AM

What is the current input voltage and frequency as seen by the UPS via Power Chute Software? If you have RMS Multimeter measure the outlet and compare the same.

 

You may change the transfer voltage as outlined in the user manual to see if there is a change in behaviour which I have appended here:

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=KBOK-757JTT_R0_EN.p...

 

Keeping in mind if the system is operating correctly and the UPS is in battery only mode it indicates the input power is out of range.

 

Let me know what the values are and the results of changing the transfer voltage. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

HarryP
Crewman HarryP
Crewman

Posted: ‎2024-10-10 04:49 PM

In response to Teken
0 Likes
0
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-10 04:49 PM

The input voltage drifts between 100 and 105 according to Power Chute; I don't have a Multimeter.

 

In the Configuration/Voltage setting I have the UPS set to intervene if the voltage is less than 97 or over 139 and for Sensitivity I currently have it set to LOW using Power Chute; it was previously set to MEDIUM because when I had it at HIGH it wouldn't stay on AC power. I've been running it at MEDIUM for about a year.

 

When I pressed the power button for 10 seconds, all of the lights flashed and then the yellow light flashed 8 times. Not sure what that means. Pressing the power button at that point simply caused the unit to switch on. When I tried this I had the data cable removed from the unit and switched back to my computer, if that would have an impact.

Reply

Link copied. Please paste this link to share this article on your social media post.

HarryP
Crewman HarryP
Crewman

Posted: ‎2024-10-10 05:01 PM

In response to Teken
0 Likes
4
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-10 05:01 PM

Well here's something interesting. While switching the data cable between my XS1200 and my newer UPS, the newer one reports an input voltage of 124 while the BX1200 reports it fluctuating around 103 and 105.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-11 04:42 AM

In response to HarryP
0 Likes
3
1429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-11 04:42 AM

You’re going to need to purchase or borrow a True RMS Meter to see what the input voltage / frequency is.

 

As the system has detected a out of range voltage, frequency, THD, or what people call dirty power. 

Let me know the results 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

HarryP
Crewman HarryP
Crewman

Posted: ‎2024-10-14 06:53 PM

In response to Teken
0 Likes
2
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-14 06:53 PM

I think my older ups needs servicing. The newer ups is reporting an input voltage near my expected 120 volt supply. Most likely some capacitors in my old unit have started to fail. Any idea where I can get it serviced? I can't find anything on the APC web site that deals with this. Very poor product support if you ask me.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-15 02:19 AM . Last Modified: ‎2024-10-15 02:19 AM

In response to HarryP
0 Likes
1
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-15 02:19 AM . Last Modified: ‎2024-10-15 02:19 AM

Given your unit is 12 years old it would make little sense in repairing the system.


If this is something you’re interested in doing any electronic repair shop can repair the unit.


You’ll need to balance the cost vs value in doing so as the APC FAQ as provided here notes the service life of their hardware is 7-10 years depending upon model.

 

This is where the hardware should be considered for a replacement or what the industry calls a hardware refresh. 👍

 

https://www.apc.com/ca/en/faqs/FAQ000265093/

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

HarryP
Crewman HarryP
Crewman

Posted: ‎2024-10-18 04:46 PM

In response to Teken
0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-18 04:46 PM

Thanks for your input. This item can now be closed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore