Posted: 2025-10-15 03:09 PM . Last Modified: 2025-10-15 03:15 PM
BX2200MI - max 1200W unit (line interactive)
Brought to safeguard a coffee machine electronics fed off genset power & for genset changeover where idle W (not making coffee) will be way below 1200W.
My thinking was i'm not going to using the coffee machine whilst the unit is running on battery so that unit should do BUT later i see there is an "online overload" alarm mentioned in the manual.
Whilst on mains power if the UPS is asked for 1450W passthru what's likely to happen?
a) online overload alarm but likely stay online or
b) likely pop the input circuit breaker
any thoughts please? - was like megabucks more to go to a higher rated unit
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-16 12:12 AM
Hi, JohnG3
APC, SE, It is not recommended to connect a coffee maker to an APC UPS because most UPSs are not designed to handle the high power demands required by appliances that use resistors, such as coffee makers and toasters. Connecting a coffee maker could overload the UPS, damage it, and, in the worst case, cause a fire, since the UPS is only for use with critical computer equipment.
The maximum load you should connect based on the apparent or real load of a UPS would be 70/80% maximum.
Video: Why might my APC Back-UPS product be beeping?
https://www.se.com/us/en/faqs/FA158827/
Best regards,
Jim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-16 03:07 AM
A Type 3 surge protector (SPD) would be a more appropriate device to use instead of a UPS.
It goes without saying you’ll need to purchase a quality unit with the appropriate power / current rating / AWG gauge.
The vast majority of no name off shore products that you see on Amazon use 16 ~ 18 AWG. A 14 AWG is more than fine but highly suggest you purchase a unit that has 12 AWG so no issues meeting the 80% duty threshold especially on a 20 amp circuit.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-17 01:54 AM
Thanks Guys - decided to return it and went with an Ecoflow power station rather.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-22 06:15 AM
The EcoFlow is a battery powered inverter generator and may meet your needs as it relates to the coffee machine.
However, it’s not a UPS and doesn’t have the same transfer time so set reasonable expectations as it relates to connecting mission critical network related hardware especially any servers that rely on a graceful shutdown to be initiated which the EcoFlow can’t handle.
Questions Ask . . . 👍