New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
UPS run time does not match with actual time
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-1706:47 AM
UPS run time does not match with actual time
Hello,
I bought the APC BXMI2200VA model recently and It shipped 100% full when I plug it into my pc and check with powerchute, I see that it shows as 100%.
Than I made a test with only modem router connected which is comsuming 12W it shows 0 load on app and for estimated time it says 67 minutes. Even on the box it says with 40W it should run 174 minutes which is 3 time longer then my app says. What can be the problem? Does it needs to discharge and charge couple times to give exact time output or does it have a minimum watt level for draining?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-2204:30 AM. Last Modified: 2025-10-2204:31 AM
Both the wattage and runtime displayed are (estimates) and not based on actual factual data.
The minimum load is approximately 120 watts before the system will reflect something coming close to reality. Place a known load you’ve validated say 500 - 1500 watt light, heater, etc
The reported wattage & current will become more accurate vs a very low load such as your modem.
NOTE: APC does not use high accuracy (wide range) CT / shunt resistors to measure the amperage / current in their systems! 🤦♂️