Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

What is my best option

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • What is my best option
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:20 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
6
1688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:20 AM . Last Modified: ‎2024-03-22 02:37 AM

What is my best option

I am building a new system and will need a new UPS. I cant seem to figure out what I will need minimum. I now have an APC ES 725. It is several years old and the battery is pretty much dead. I will want to run 2 computers so if its is possible to get one that will hook to shut 2 units down that would be great. My old system- Asus A7N8X Deluxe E ,, AMD Athlon XP 2800+ Barton ,, 1Gig ram ,, BFG Tech BFGE73512GT GeForce 7300GT 512MB 128-bit GDDR2 AGP 4X/8X,, 4 hard drives ,, and a 400 wt antec smartpower.

My new system will be MSI 770-C45 AM3 AMD 770 ATX AMD Motherboard ,, Patriot G Series 'Sector 5' Edition 4GB (2 x 2GB) 240-Pin DDR3 SDRAM DDR3 1333 (PC3 10666) Desktop Memory Model PGV34G1333ELK ,, AMD Athlon II X4 630 Propus 2.8GHz Socket AM3 95W Quad-Core Processor Model ADX630WFGIBOX ,, XFX HD-577A-ZNFC Radeon HD 5770 (Juniper XT) 1GB 128-bit GDDR5 PCI Express 2.0 x16 HDCP Ready CrossFireX Support Video Card ,, 2 huge hard drives for now, maybe more later,, and a CORSAIR CMPSU-750TX 750W ATX12V .

I will be using a KVM switch and using i monitor an ASUS VW246H Glossy Black 24" 2ms(GTG) HDMI Widescreen LCD Monitor.
The more I recearch this the more confused I get. I dont care how long the battery lasts as long as it lasts long enough to shut down my comuter/s . If a unit to handle both PC's is out of reach I will just replace the battery in the one I have and buy a new one for the new PC and the monitor. I want a bare minimum expense. I already tripled my original $400 budget.

If it makes a difference my PC's will be hooked together via eithernet wire.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

I was looking at this unit APC - 1500VA Battery Back-Up System - Black
Model: BX1500G
I see it went off sale now and went from $169 to $199. I suppose I could just buy a battery for my old one or replace it for the old computer and run the new computer and monitor off the bigger one.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 02:20 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:20 AM . Last Modified: ‎2024-03-22 02:37 AM

I'd say the smallest Smart-UPS you could use is the SUA750, but you would really be pushing your luck and have to hope that the system plus any other load never reaches 500W. This would basically require the PC to not be doing anything really intensive consistently, etc. The SUA1000 would definitely work.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

The concern here is that you will have two PC's, and it sounds like you want one UPS to shut them both down. In addition, I am familiar with the quality of Corsair parts and assume their power supplies are targeted and designed for users who care about excellent system performance, etc. I checked their website for your PSU model and the PSU is active power factor correction, which can have serious issues cooperating with pretty much any unit in the "Back-UPS" family of UPS'. This is because the Back-UPS produce a stepped approximation to a real sine wave when they are on battery, and active PFC PSU's are designed to "actively" monitor, filter, and regulate incoming sine wave form anomalies in order to provide the purest power to the computer. An active PFC PSU many times is going to see a stepped approximated sine wave as a sine wave distortion, and can shut down in those cases. This is unfortunately entirely dependent on the PSU and configuration of load as sometimes we find that a customer has used a Back-UPS product for a few years with no issues, and other times it is totally incompatible. We have made engineering changes to the Back-UPS line to be more compatible with active PFC devices, but the fact that they will always look for power fluctuations and wave form issues makes it very hard to guarantee compatibility no matter what.

The UPS' we make that are guaranteed to work with active PFC are our Smart-UPS products (SUA type). They output a pure sine wave. They are more expensive so you may need to go with your plan of using two UPS'. A single 750w power supply will pretty much bring any Back-UPS product pretty close to its load limit, same thing for the cheapest Smart-UPS product we offer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

The BX1500G wattage rating would be just fine for the computer you specified, the only thing I would be concerned about is if it is compatible with an Active PFC device. If it does not work because of this fact/concept and this is determined to be the reason, we can't do an RMA for it or waive any return/restocking fees.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

OK I bought the BX1500G from best buy because they will let me return it. I have had it a couple days and decided to put it to the test tonight. I unplugged it and I could swear I heard a slight buzzing noise from the PC. But it kept it running the full five minutes then hibernated it. Although The USB connection was lost for a second or 2 twice. The problem came when I plugged it back in. Maybe I should have let it charge a few minute before turning on the computer. I turned on the computer and after about a minute the ups gave a warning beep beep just like when it was unplugged And about 30 seconds later my PC shut off without shutting down. I waited a couple more minutes and no more beeps so I tried again. This time every thing is fine. I think I will return it and put the money towards an SUA. Is there a model between the SUA750 and SUA1000. I think 600 watt would be enough. This one had plenty of reserve after 5 minutes.
I would like to trade up and send in my Back-ups ES 725

I just tried it again and My room mate tells me I need to wait for every thing to reset. I did and it did and every thing looks hunky dory so maybe Im ok after all. I think the buzz I heard was from the UPS its self.

Message was edited by: sidmabb

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

I am building a new system and will need a new UPS. I cant seem to figure out what I will need minimum. I now have an APC ES 725. It is several years old and the battery is pretty much dead. I will want to run 2 computers so if its is possible to get one that will hook to shut 2 units down that would be great. My old system- Asus A7N8X Deluxe E ,, AMD Athlon XP 2800+ Barton ,, 1Gig ram ,, BFG Tech BFGE73512GT GeForce 7300GT 512MB 128-bit GDDR2 AGP 4X/8X,, 4 hard drives ,, and a 400 wt antec smartpower.

My new system will be MSI 770-C45 AM3 AMD 770 ATX AMD Motherboard ,, Patriot G Series 'Sector 5' Edition 4GB (2 x 2GB) 240-Pin DDR3 SDRAM DDR3 1333 (PC3 10666) Desktop Memory Model PGV34G1333ELK ,, AMD Athlon II X4 630 Propus 2.8GHz Socket AM3 95W Quad-Core Processor Model ADX630WFGIBOX ,, XFX HD-577A-ZNFC Radeon HD 5770 (Juniper XT) 1GB 128-bit GDDR5 PCI Express 2.0 x16 HDCP Ready CrossFireX Support Video Card ,, 2 huge hard drives for now, maybe more later,, and a CORSAIR CMPSU-750TX 750W ATX12V .

I will be using a KVM switch and using i monitor an ASUS VW246H Glossy Black 24" 2ms(GTG) HDMI Widescreen LCD Monitor.
The more I recearch this the more confused I get. I dont care how long the battery lasts as long as it lasts long enough to shut down my comuter/s . If a unit to handle both PC's is out of reach I will just replace the battery in the one I have and buy a new one for the new PC and the monitor. I want a bare minimum expense. I already tripled my original $400 budget.

If it makes a difference my PC's will be hooked together via eithernet wire.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

I was looking at this unit APC - 1500VA Battery Back-Up System - Black
Model: BX1500G
I see it went off sale now and went from $169 to $199. I suppose I could just buy a battery for my old one or replace it for the old computer and run the new computer and monitor off the bigger one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore