Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

What determines the shut down ?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • What determines the shut down ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:42 PM . Last Modified: ‎2024-03-20 03:55 AM

0 Likes
4
1408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:42 PM . Last Modified: ‎2024-03-20 03:55 AM

What determines the shut down ?

I have a Back-UPS XS 1300, and I have  larger capacity batteries then came with this unit.  What determines the shut down, does it assumes it has two 9ah batteries, and looks at the time factor, or does it look at battery voltage ?

The software does not provide any way to adjust for longer battery time.

Also on a side note, it is very annoying that this unit has a known problem with LCD dimming, and even in the dark, very difficult to read.  It would be nice if such a part was available, so I could replace, and yes I'm Tech.

I have no other complaints about these units, other then replacing batteries, and the dim LCD, they have been working fine, I have two of these units.

Roy

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

0 Likes
0
1408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

Hi again Roy,

After checking and trying to better understand this myself to explain to you, the most accurate runtime will be seen when the UPS is on inverter supplying power to the attached load. This runtime is dynamic and adjusts as load is added or reduced, in relation to the preset battery constants in the UPS EEPROM. This constant is set at the factory for the battery being shipped with the UPS and can not be altered in the field. The constant adjusts over time, as the battery discharges and recharges in an effort to provide the most accurate runtime. The only other option which we don't know if it will work or not for what you need will be a runtime calibration. If anything, I suspect there is a maximum runtime the UPS will report based on a brand new battery (referring to the included 9AH battery) and if anything, it could report that max value to you at least based on a full capacity 9AH battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

0 Likes
0
1408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

Hello Roy,

I inquired about the runtime and was told that the UPS calculates runtime based on the capacity of it and the rate of discharge in relation to the AH of the original battery. Back UPS are not too flexible as allowing the user to add external, third party battery packs in like some of the larger UPS models are unfortunately. We only had a few models that supported their own APC external battery packs that I know of. I think even those only supported two because then the internal UPS charger can't keep up which is another concern of adding your own external batteries since the UPS charger is sized for the original battery size.

As for the LCD, it seems as though there was a firmware adjustment at some point to extend the life of the LCD and likely dim it a little bit to help it last a little longer overall. While you may be experienced with replacing the LCD, the smaller UPSs usually don't have serviceable parts like this (outside of the battery module) because majority of the install base is not experienced with this type of replacement and I am sure the company won't want to be liable for people doing this and damaging something or hurting themselves. I imagine the cost of making the part safe to replace for all users is not worth it for a smaller UPS but I am just making an educated guess on that comment along with my personal opinion.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

0 Likes
0
1408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

Thanks for the info, I kind of knew that it was the way it determined the run time, I was just hoping.  The question is now, how does it reset ?

Does it reset when line voltage is reapplied, and does it look at its charging time to know what amp hours are available for the next time.  I have two 100ah AGM batteries connected, they were left over from an another project, I tested the charging voltage and it's right on the button. 

I realize that APC does not want to deal with people repairing their own stuff, but I'm a 70 old technician and have been repairing electronic stuff most of my adult life.  Its a shame that such activity is no longer encouraged, for there is a lot to learn with such activity, I guess I'm getting up in age, and don't like to accept we have become a buy and throw away society.

Roy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

0 Likes
0
1408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

Hi Roy,

I'll have to check into it further. The person I want to ask that may know has left for the day so I'll report back on Monday I hope. I am not sure how it resets specifically.

I agree what you said in your last paragraph. It is kind of sad frown

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

0 Likes
0
1409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:43 PM . Last Modified: ‎2024-03-20 03:55 AM

Hi again Roy,

After checking and trying to better understand this myself to explain to you, the most accurate runtime will be seen when the UPS is on inverter supplying power to the attached load. This runtime is dynamic and adjusts as load is added or reduced, in relation to the preset battery constants in the UPS EEPROM. This constant is set at the factory for the battery being shipped with the UPS and can not be altered in the field. The constant adjusts over time, as the battery discharges and recharges in an effort to provide the most accurate runtime. The only other option which we don't know if it will work or not for what you need will be a runtime calibration. If anything, I suspect there is a maximum runtime the UPS will report based on a brand new battery (referring to the included 9AH battery) and if anything, it could report that max value to you at least based on a full capacity 9AH battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore