UTS6H - load phases and neutral bond?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS6H - load phases and neutral bond?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
5
1085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

UTS6H - load phases and neutral bond?

First, my apologies for asking questions that have probably been asked before.  I tried the search function but it does not appear to be working right now.

I'm about to install a UTS6H to use with either my EU3000is or two paralleled EU2000is's.  I own all three generators.

I was excited to discover this innovative product that will accept a 120V generator input, but I have two questions.

The UTS6H will support six 120V loads.  Can these loads be from both phases of the main panel?  What are the rules, if any, about selecting and balancing the 120V loads?

Second question.  Where is the neutral bond when under generator power?  The neutral bond is in the main panel under utility power and should be (I think) in the UTS6H when under generator power.  I'd appreciate an explanation of the UTS6H design and the neutral bond.

Thank you!!!!

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • bond
  • neutral
  • phases
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

According to APC, the various UTS models don't require bonding because of their use of fuses, rather than resetable circuit breakers, like those found in most home panels, as overload protection devices.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

OK, I've been clicking around here and have answered my second question myself.  Neutral and ground are separated in the UTS6H and the neutral to ground bonding remains in the main panel.  This is a different electrical architecture than with a conventional manual transfer switch and sub-panel where the neutral bond must be made in the sub-panel under generator power and lifted in the sub-panel when under utility power.

It's taken me a while to grasp what the UTS6H actually is.  What it's not is a sub-panel.  It is in effect part of the main panel with (solid state?) relays in series between the load side of the main panel breakers and the load.  These relays can feed the load with either utility power or backup power from a generator or from a UPS.

I assume the designers of the UTS6H selected relays that have no failure mode that would allow backfeeding of generator power to the utility side of the main panel.  I would hope so anyway.  In the case of a power outage I will probably shut off the main panel breaker and the six load breakers anyway though I can see from the documentation none of that should be necessary.

Now I understand this I guess I can also answer my first question.  The six UTS6H circuits can be installed on any 15A or 20A breakers in the main panel regardless of phase as the loads don't care which leg of the main panel the breaker is installed on when they're being fed with generator power via the relays in the UTS6H.

If I have any of this wrong please jump in with a correction.  Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

"This is a different electrical architecture than with a conventional manual transfer switch and sub-panel where the neutral bond must be made in the sub-panel under generator power and lifted in the sub-panel when under utility power."

Bonding normally doesn't occur in the manual transfer switch as when on utility power, the neutral and ground wires in the manual transfer switch lead back to the main panel where such bonding between the neutral and ground buses occur.

I may be mistaken but under generator power isn't that bonding happening in the generator itself?

"I assume the designers of the UTS6H selected relays that have no failure mode that would allow backfeeding of generator power to the utility side of the main panel.  I would hope so anyway."

The UTS6H's UL-1008 certification mandates that such backfeeding (i.e. why we have a transfer switch, manual or automatic in the first place) cannot occur. Isolation of the generator load from the utility load is mandatory, never shall the two cross paths, at least in not only most transfer switches, but definitely those UL-1008 certified as this one is.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

I'd like to clarrify some things.  First of all the purpose for bonding: it ties back to the circuit breakers in the main panel being able to work propertly, but determine the rapid change in electrical potential in a circuit, that is best detected when neutral and ground are connected in the main panel only.

For [portable] generators like the Honda inverter, the circuit on this device is your main panel, so to speak when you are running off of it in a power outtage.  Sadly, most portable generator manufacturers have what's called a floating neutral, or one where neutral and ground aren't connected, even though they should.

The user can made this happen my making an "Edison" plug,

http://ricksdiy.com/generators/portable-inverter-generator-neutral-ground-bonding-plug-honda-yamaha/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

ok, yet another caveat.  The wiring diagrams for all the APC UTS' suggest not bonding the generator.  Perhaps the UTS does this when working off of generator power only.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 PM . Last Modified: ‎2024-03-21 03:58 AM

According to APC, the various UTS models don't require bonding because of their use of fuses, rather than resetable circuit breakers, like those found in most home panels, as overload protection devices.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of